I have an electric heater which I will connect to a contactor and a 24 volt 2 pole themostat. I am searching for a 120V to 24 volt plug in type transformer and I am confused. I see 24 volt AC transformers, all with VA (volt amps) specs. Some are at 20VA, some at 40VA and 50VA. How important is the VA and how should it influence my thermostat choice?
Captflx is offline   Reply With Quote
Old 01-27-2010, 10:34 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,006
In very basic terms VA is equivalent to watts.
Old 01-27-2010, 11:06 PM   #3
You would need to match the VA to the requirments of the contactor. 24 volt 20 VA would supply 24 volts at .8 amps, 24 volts 40 VA would supply 24 volts at 1.7 amps.
hayewe farm is offline   Reply With Quote
Old 01-28-2010, 12:54 PM   #4
Rewards Points: 113
VA (volt amps)
hayewe farm---in A=(VA*PF)/V, what power factor are you using or did your amps results come from a table? also what is the value of V? 24 volts?
Thanks!
Old 01-28-2010, 06:14 PM   #5
VA =volts times amps. 24 volts times .8 amps =19.2 VA I did round the amps it should be .83333333333333 amps.
Old 01-28-2010, 06:47 PM   #6
Rewards Points: 113
VA (volt amps)
Thanks for your help.
Old 01-29-2010, 10:55 AM   #7
Wire Chewer
Red Squirrel's Avatar
Rewards Points: 528
Are you sure that's what it is? I see UPSes and transformers rated in VA's all the time but the wattage is actually a bit lower. For example I have a 1 KVA UPS at home but it's actually 600W max. I've always wondered how VA's work as some stuff is rated in them.
Old 01-29-2010, 01:06 PM   #8
Rewards Points: 2,800
The industry standard for rating small UPS units (1000 VA or so, or smaller) is to give a VA rating 65% greater than the watts rating, or a watts rating 60% of the VA rating.
AC equipment containing coils or capacitors is likely to draw amperes at a given voltage so that VA is greater than the watts consumed. The ratio of watts to VA is called the power factor. Personal computers often have a capacitor power supply and a power factor in the 60% range.
For DC equipment and for AC equipment that is purely resistive (such as non-motorized heaters and incandescent lights) VA equals watts, or the power factor is 1.
You may not exceed the watts rating of the UPS or transformer.
Stick to your lawn watering schedule until it really starts to pour. After the storm you have only the same number of rest days you always had and then you need to start watering again.
Old 01-29-2010, 02:15 PM   #9
Electrical Contractor
kbsparky's Avatar
You could get one of these units, which has the transformer, and relay built-in.
-KB
240 volt single phase 38 max amps heater made by patron williestyles08 Electrical 8 01-06-2009 10:20 PM