I was replacing floodlights over my garage door today and noticed that someone had cheated and just screwed them into siding and run a lamp cord through a hole. I fixed this by installing a box and used armored cable instead of lamp cord.
Whoever did this before used the neutral wire of the lamp cord to feed the neutral of the lights and the ground wire. They just wire nutted them together. Was this common with outdoor lighting? It doesn't seem right to me because the whole fixture would become dangerous if the neutral became loose somewhere.
sroad is offline   Reply With Quote
Old 12-16-2016, 12:02 AM   #2
dmxtothemax's Avatar
Rewards Points: 7,664
Re: Using Neutral as Ground
it was accepted practice in the past,
but not any more.
as you surmise, if neutral is lost
then potentially earth becomes live.
dmxtothemax is offline   Reply With Quote
Old 12-16-2016, 07:06 AM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,006
but not any more.
Actually this was never accepted practice, at least in the US, except for two specific exceptions. Older dryers and ranges, and older feeders to detached structures.
Bootleg ground and neutrals are NEVER legal or safe on other branch circuits.
jbfan, joed, rjniles and 4 others like this.
The Following 3 Users Say Thank You to Speedy Petey For This Useful Post:
Jim Port (12-16-2016), joed (12-16-2016), Oso954 (12-16-2016)
Backwards Neutral to Ground Bond on Sub-Panel? Mr.Natural Electrical 25 01-29-2015 10:51 AM
Ground wire from panel to ground rod swbrains Electrical 46 09-03-2014 06:05 AM
Neutral Ground Bus Bar, Will This Be A Problem Now Tyrel Electrical 9 08-25-2013 08:12 AM
3 Wire Set Up . . . Neutral Wire Tied to Ground Wires irishMonster Electrical 14 10-21-2010 09:20 AM
Ground and Neutral in Panel bvbellomo Electrical 21 07-17-2010 10:53 AM