Is There A Problem With My Standby Generator? - Electrical - DIY Chatroom Home Improvement Forum
Old 12-10-2015, 10:29 PM   #1
Rewards Points: 1,072
Is there a problem with my standby generator?
I have a 3 year old Generac 8kw standby generator. Today we had a power outage. The generator came on, but I got no power.
I found there was 123v in both the wires going from the generator to the transfer switch, but there was only 3v between them; not the 240v I expected. A replay was open so no power was getting to the circuits; presumably it requires 240v.
I called the company that services it and they suggested I manually turn the generator off and back on. That fixed it. I got 240v at the transfer switch and power to my circuits. The service man said I had reflashed the coils, whatever that is. He wasn't very concerned about it. Utility power came back in 10 minutes.
Later in the day I opened the 50a circuit in my panel going to the transfer switch to simulate a power outage. The generator came on and worked normally.
So...
What happened to my generator? Is it a common problem? Does it require any service?
Toller is offline   Reply With Quote
Old 12-10-2015, 11:03 PM   #2
Super Moderator
joed's Avatar
Rewards Points: 404
The generator needs a bit of magnetism to begin generating electricity. Once it starts spinning the magnetism builds until reaches the proper amount. If the magnetism fades too low it can get started and needs to be flashed it magnetize the stator again.
This usually happen when a unit is not run long periods. Does your unit get exercised. Many units will start automatically once a week for ten minutes.
Old 12-10-2015, 11:56 PM   #3
dmxtothemax's Avatar
Rewards Points: 7,866
Go onto you tube
Search for "flash the feild"
You can do it with two drills.
dmxtothemax is offline   Reply With Quote
Old 12-11-2015, 06:38 AM   #4
Rewards Points: 2,084
So...
Run it for several minutes every few weeks and it should be ready when you need it.
John Grabowski
MrElectrician.TV
MrElectricianTV is offline   Reply With Quote
Old 12-11-2015, 09:58 AM   #5
It runs for 10 minutes every week, but it doesn't power anything
So, this is just something that happens and I shouldn't be concerned about it?
Old 12-11-2015, 10:48 AM   #6
Super Moderator
joed's Avatar
Rewards Points: 404
It is rare but it should not be happening.
Old 12-11-2015, 03:49 PM   #7
If your generator is getting its regular exercise and you have this issue, then you might have a problem.
John Grabowski
MrElectrician.TV
Old 12-11-2015, 04:30 PM   #8
Running the geeny unloaded may stop the
Motor gumming up
But it will not help the alternator !
You need to run it loaded.
Otherwise the residual magnatism
of the feild will fade away.
The only way to keep it up
is to run current thru it regularly.
Whole house standby generator - Generac vs. Milbank nwohioguy74 Electrical 7 02-03-2013 12:13 AM
Generator: Floating the neutral AdamBNYC Electrical 30 12-08-2012 02:18 PM
Champion 7000/9000 Watt Costco Generator wiz561 General DIY Discussions 8 11-24-2012 05:24 PM
Standby Generator & Transfer Switch JRoot Electrical 9 06-12-2011 09:14 AM
Standby generator connected via detached garage? vsheetz Electrical 22 04-04-2009 02:44 AM