Here is a poser that has been solved. I just want to see what others think
One split wired receptacle on the circuit. Only half of the receptacle works.
Voltage at breaker from each terminal to neutral is 120 volts with a proper wiggy meter.
Swap black and red at breaker same problem.
Disconnect black and red short together at one end. Ohms as connected.
Measure voltage across breaker with wires off 240 volts.
Old 02-24-2019, 04:39 PM   #2
hkstroud's Avatar
Rewards Points: 6,684
Re: split receptacle half dead
A double breaker?
Harold,
The Left Handed Widget Maker
hkstroud is offline   Reply With Quote
Old 02-24-2019, 04:45 PM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 802
Tab is open between the neutral screws at the receptacle.
My electrical answers are based on 2017 NEC, you may have local amendments.
Old 02-24-2019, 05:09 PM   #4
Super Moderator
joed's Avatar
Double pole breaker.
More clues for you.
Move wires to another DP an all is well.
Put wires onto breaker and only measure 87 volts. Measured 240 with no wires. Current check show 0 amp current on both wires.
Old 02-24-2019, 05:49 PM   #5
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 1,744
Joed.... What do you mean by "Ohms as connected"
Do you just mean a very nominal/small ohms reading consistant with normal continuity.?
MTN REMODEL LLC is offline   Reply With Quote
Old 02-24-2019, 06:09 PM   #6
Rewards Points: 2,050
More clues for you.
Is that 87V measurement under a load, or just with wires connected but no load at the receptacle?
I'll guess there is a high resistance on one set of contacts inside the breaker.
RAL238 is offline   Reply With Quote
Old 02-24-2019, 06:18 PM   #7
Will yo tell us about the loads on the black and red circuits...??? and how they got in series...???
Old 02-24-2019, 06:28 PM   #8
Super Moderator
joed's Avatar
No loads.
Old 02-24-2019, 06:30 PM   #9
Old 02-24-2019, 06:31 PM   #10
Super Moderator
joed's Avatar
Shorted as expected. It was a test to see if one of the wires was open. Test showed continuity of both red and black wires.
MTN REMODEL LLC likes this.
Old 02-24-2019, 07:36 PM   #11
Super Moderator
joed's Avatar
The problem was a bad breaker. I will cut it open see what it looks like.
It was an odd problem to find. I even took the breaker out an measured each side for continuity. Something strange about when I attach the wires and voltage across the poles went to 87.
Old 02-24-2019, 07:50 PM   #12
Super Moderator
joed's Avatar
Here it is. Someone at some time had a dead short, possibly more than one.
Since this is a split wired receptacle I would guess someone who didn't know better probably replaced it without cutting the tab and tried several times resetting it.
I would say that was probably true.
Old 02-24-2019, 07:57 PM   #13
Super Moderator
joed's Avatar
Do you think I could file the points and put it back together?
Old 02-24-2019, 09:09 PM   #14
Msradell's Avatar
Rewards Points: 1,094
You are kidding aren't you?
Written using Dragon Naturally Speaking
Msradell is offline   Reply With Quote
Old 02-24-2019, 09:25 PM   #15
Super Moderator
joed's Avatar
Of course.
Hence the smilies.
One duplex receptacle split to be controlled by 2 switches pex006 Electrical 52 04-02-2014 12:10 PM
230v from split unit a/c to receptacle Def.Eah Electrical 12 06-15-2013 08:52 PM
split receptacle on three way switch suseagulls Electrical 17 08-05-2010 11:08 AM
how to wire romex to 2 3 ways to a half hot receptacle smoothinstall Electrical 3 11-30-2008 10:56 PM
Half Dead Tree handy man88 Landscaping & Lawn Care 11 06-30-2008 11:21 PM