Silly Amperage/voltage Question - Electrical - DIY Chatroom Home Improvement Forum
Old 01-09-2010, 09:48 PM   #1
Wire Chewer
Red Squirrel's Avatar
Rewards Points: 586
Silly amperage/voltage question
When sizing a breaker for a specific appliance, lets say the appliance uses 3000w and plugs into 240V, would a 15 amp double pole breaker do? Since 15x240 is 3600w So while it will only give 1800w on a single leg at 120v it will give 3600w at 240v, so technically the 3000w device should only pull 12.5 amps right?
Also 14awg would still be the minimum wiring used correct?
I don't have anything specific I'm working on though I do have a plan where this might come to play so it's more or less a theoretical question at this point.
Old 01-09-2010, 09:53 PM   #2
Electrical Contractor
kbsparky's Avatar
A 15 Amp 240 Volt circuit can supply a 3600 watt load .... but ...
If it's a continuous load the maximum on a 15 Amp circuit would be 2880 watts. This assumes a power factor of 100%, such as for electric resistance heating. If you have motor or other loads that operate on a lower power factor, then you will have to factor that into your calculations as well.
Note: Circuits for electric heating units are required to be sized at 125% of the connected loads.
-KB
Old 01-09-2010, 10:01 PM   #3
Wire Chewer
Rewards Points: 586
Yeah makes sense, you want to size higher. So in a real case scenario a 20 amp breaker would be better to use I guess.
Old 01-09-2010, 10:01 PM   #4
Current is equal to the wattage, divided by the applied voltage!
I=P/E I=3000/240 I=12.5 amps
A double pole, 15 amp breaker on #14 wire is adequate. However, on a long run #12 would be better!
Old 01-10-2010, 08:22 AM   #5
kbsparky's Avatar
Originally Posted by Wildie View Post
.... A double pole, 15 amp breaker on #14 wire is adequate.....
Not for continuous loads!
Article 100.I Definitions
Continuous Load. A load where the maximum current is expected to continue for 3 hours or more.
210.19(A). Branch circuit conductors shall have an ampacity not less than the maximum load to be served. Where a branch circuit supplies continuous loads ... the minimum conductor size ... shall have an allowable ampacity of not less than ... 125 percent of the continuous load.
424.3(B) ... Fixed electric space heating equipment shall be considered continuous load.
The bottom line is dependent on what is connected to the circuit as whether is is adequate or not.
-KB
Old 01-10-2010, 08:40 AM   #6
Inspector/Instructor
codeone's Avatar
So your circuit would be
I=P/E I=3000/240 I=12.5 amps x 125% = 15.625 amps = 20 Amp Circuit
codeone is offline   Reply With Quote
Old 01-10-2010, 10:21 AM   #7
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,006
VERY little in a home is, or could/would be, considered a continuous load.
Electric heat and waters heaters are two automatic examples.
Old 01-10-2010, 08:57 PM   #8
Wire Chewer
Rewards Points: 586
Glad I was on right track. I was not taking into account other factors like continuous load requirements etc, was thinking mostly just in theory. In a real life situation I'd put such load on a 20 amp circuit and use 12 awg or even 10 awg wiring just to be on the safe side.
Old 01-10-2010, 09:57 PM   #9
Super Moderator
joed's Avatar
Rewards Points: 32,366
The one other consideration you need to consider is the manufacturers direction for installation.
Old 01-10-2010, 10:02 PM   #10
Exclamation
With #12 AWG wire all the way. (Only common sense.)
spark plug is offline   Reply With Quote
Simple electrical question (Amperage/voltage) Badfish740 Electrical 18 01-06-2009 11:35 AM
Basement Renovation Question KUIPORNG Remodeling 234 08-26-2008 08:19 AM
may be a silly question, but..... DangerMouse Electrical 20 07-21-2008 07:20 PM
hrv question indep HVAC 3 07-17-2008 10:39 PM
One furnace question and one thermostat question lh0628 HVAC 4 10-11-2007 10:17 PM