Short Run Of Romex Outdoor, Conduit Ok? - Electrical - DIY Chatroom Home Improvement Forum
Old 01-05-2010, 05:48 PM   #1
Short run of romex outdoor, Conduit ok?
I need to run two new circuits of 8/2 from my distribution panel to a new tankless water heater in my garage. Each run is about 75'.
My distribution panel is mounted on the surface of my (brick) exterior wall, so I don't think that it would be possible for me to fish any new wire up there.
The top of my panel is about a foot below my soffet, so I was thinking that I could stick a small piece of conduit in that space and just pull the new romex through it, up into my attic space, and then over to my garage where the water heater will be installed.
Any thoughts?
I'm guesstimating that 1-1/2" conduit would be big enough.
Is ENT suitable or would I need EMT?
Spaceball1 is offline   Reply With Quote
Old 01-05-2010, 05:51 PM   #2
If romex is outside it must be rated for wet installation, even in conduit
Is the garage (fully) attached to the house (I'm thinking yes) ?
Old 01-05-2010, 05:55 PM   #3
Is the garage attached to the house ?
Even if it's in a location where it can't get wet? Dang.. So I need UB Romex?
Yes, the garage is attached and the water heater will be mounted on the wall. I'll use the leftover conduit to route the romex down the wall to the disconnects.
Old 01-05-2010, 06:19 PM   #4
That's usually the case...even just for 1'
Some might just do it anyways....but I'd check with the inspector 1st
Old 01-06-2010, 11:14 AM   #5
Just call me Andrew
Rewards Points: 1,032
Is there a reason he can't just use individual strands THWN wire inside the conduit?
Andrew
secutanudu is offline   Reply With Quote
Old 01-06-2010, 11:54 AM   #6
Master Electrician
richgriffith's Avatar
yes you can run individual strands of THWN in P.V.C. run four No.8 Feeder conductors & one NO.6 Ground. and you can use 1'' P.V.C. conduit.
richgriffith is offline   Reply With Quote
Old 01-06-2010, 03:26 PM   #7
Inspector/Instructor
codeone's Avatar
What you can do is run conduit up to your attic set a J-box for the conduit to terminate into,run THWN to the j-box then chacge over to NM (romex) cable. This would be code compliant.
Now are you sure you only need #8 NM. What is the current draw for each circuit?
codeone is offline   Reply With Quote
Old 01-06-2010, 04:43 PM   #8
Originally Posted by richgriffith View Post
yes you can run individual strands of THWN in ENT. run four No.8 Feeder conductors & one NO.6 Ground. and you can use 1'' ENT.
ENT outdoors?
jerryh3 is offline   Reply With Quote
Old 01-06-2010, 07:09 PM   #9
Master Electrician
look in your 2008 code book. article 362.10 you can run ENT exposed outdoors.
Old 01-06-2010, 07:25 PM   #10
I did. It only says it can be used in wet locations indoor, in a concrete slab, or below grade.
Old 01-06-2010, 07:27 PM   #11
Master Electrician
P.V.C pipe is what i meant sorry. what the h#ll is ENT? is that like the flexible stuff. never use it. my bad didn't mean to miss lead anyone.
Old 01-06-2010, 07:31 PM   #12
Ok. That makes more sense. ENT is smurf tube. RNC is hard PVC conduit.
Old 01-06-2010, 07:46 PM   #13
Master Electrician
ok, yeah i think i used it once or twice along time ago to pull low voltage through. like i said got the two mixed up. Electrical nonmetallic tubing i always thought they were referring to pvc. well im glade to know that. too error is human my friend.
Old 01-07-2010, 03:27 AM   #14
Electrical Contractor
kbsparky's Avatar
According to my charts, a #10 ground would be acceptable.
-KB
romex clamped against bx knockout in old box kbm774 Electrical 11 08-16-2010 01:53 PM
OK to do a short, unsupported, vertical run of romex in finished wall? TomServo Electrical 2 10-04-2009 07:43 AM
Connecting Romex at Panel Bocolo Electrical 14 02-21-2009 05:55 AM
Cost Difference Between Conduit & Romex Shawns4 Electrical 39 08-25-2008 05:01 PM
Romex to BX fifaboy Electrical 1 02-27-2005 04:12 PM