SER Or SEU - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-26-2009, 09:19 PM   #16
Thanks Speedy, So under the 08 code I can set a meter base combo outside and feed my ac outside then run a Ser 4/0 Al cable to my 200 amp panel inside.
Just like the 05 code.
Some people we're telling me I needed conduit and single strand 4/0 al.
Is this because of the derating percentages.
This is a duplex
Penczak is offline   Reply With Quote
Old 10-26-2009, 09:23 PM   #17
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,006
Regardless of any changes to the code, I have NEVER heard of SER being red tagged for this.
If you have been hearing this I would definitely check with your local authority though.
Yet ANOTHER stupid 2008 NEC change!
Old 10-26-2009, 09:34 PM   #18
Thanks, I see why they call you Speedy
Old 10-27-2009, 08:04 AM   #19
Licensed electrician
Rewards Points: 3,746
With this setup the 4/0 would not be feeding the entire load of the dwelling and would need to be sized per 310.16, not 310.15(B)(6).
Ironic that you can take a portion of the load off and need to run larger conductors.
Old 10-27-2009, 07:36 PM   #20
But if it is feeding the whole load. It (SER) does not require conduit, right?
Old 10-27-2009, 10:28 PM   #21
How do you figure Jim? We are talking about between a main disconnect and the main distribution panel, right? Or am I missing something?
You'd be technically right if it were a feed through panel outside.
Again, it is completely absurd that this change ever made it in. I still cannot see why or how they could justify requiring a feeder cable be larger conductor than the service entrance cable.
Old 10-27-2009, 10:45 PM   #22
My thoughts are that they did not intentionally do this. But people we're doing there bare minimum for sub panels.
Such as the 6 two pole breaker panel with no main. Lot a guys would run the entire branch circuits and the dryer with #2 Al on a 90 amp breaker.
I hear that it will be worded different in the 2011 NEC
Old 10-28-2009, 09:22 AM   #23
Rewards Points: 322
I asked the city inspector here the same question. He said for the main feed from the pole, the poco gets to decide what is code. For the wiring between disconnect and distribution panel, this is residential wiring, so the city gets to decide what is code. He felt the poco here always undersizes their feeds, so I was not allowed to use the same SER for my 200A panel to panel connection. I believe the poco is planning to use 2/0 al, and I had to use 2/0 copper THHN.
tns1 is offline   Reply With Quote
Old 10-28-2009, 11:26 AM   #24
2/0CU is the standard size for a residential 200A service entrance.
Old 10-29-2009, 10:17 AM   #25
Pete,
He said the AC was being fed from a seperate breaker at the disco with another breaker feeding the panel in the house. Thus the SER is not serving the entire load of the dwelling.
This is a duplex
Old 10-29-2009, 01:20 PM   #26
Pete,
So is 4/0 SER good. No conduit
Old 10-29-2009, 05:45 PM   #27
Pete,
I guess some inspectors are being sticklers about this obvious aberration of the code.
I would still run 2/0cu or 4/0al. Common sense tells me there is ABSOLUTELY NO REASON to run a larger feeder than the service entrance conductors.
Old 10-30-2009, 09:40 PM   #28
Is conduit required ?
Old 10-31-2009, 06:35 AM   #29
Not for SE cable unless it is a sleeve for protection.