SER Cable Touching Insulation 1 Side - Derate? - Electrical - DIY Chatroom Home Improvement Forum
Old 06-01-2015, 07:38 PM   #1
Rewards Points: 4
SER cable touching insulation 1 side - derate?
Hello,
I am going to be installing a subpanel in my attached garage in the near future. Currently the wall is 2x4 stud wall with insulation stalled. I plan on scabbing on 2x3s to allow me to flush mount the panel and have a void in which to run my Romex through without having to fight insulation.
Where my service entrance cable enters from it will be in contact with 1 face of the insulation, but not enveloped in it. I know the NEC allows 10 feet/10% (whichever is shorter) to be in insulation without derating the ampacity, but for it to be considered "in insulation" does it need to be enveloped or just touching insulation? Thanks.
ajssbp is offline   Reply With Quote
Old 06-01-2015, 08:04 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 6,812
Dont know where you got the 10'/10% from, but derating not necessary.
Yes I am a pirate, two hundred years too late
The cannons don't thunder, there's nothing to plunder
I'm an over-forty victim of fate.
jbfan is online now   Reply With Quote
Old 06-01-2015, 08:27 PM   #3
Rewards Points: 4
I don't have direct access to the NEC, but this is what spurred my question:
For interior branch circuits and feeders, Section 338.10(B)(4)(a) limits SE cable run through insulation to be limited to its ampacity in the 60°C column of Table 310.15(B)(16). Note that Section 310.15(A)(2) Exception allows up to 10 feet or 10% (whichever is less) to run through insulation without limiting the SE cable to 60°C.
http://iaeimagazine.org/magazine/201...able-310-15b7/
Old 06-02-2015, 12:37 PM   #4
Rewards Points: 422
310.15 Ampacities for Conductors Rated 0–2000 Volts
(A) General.
(2) Selection of Ampacity. Where more than one ampacity
applies for a given circuit length, the lowest value shall be used.
Exception: Where two different ampacities apply to adjacent
portions of a circuit, the higher ampacity shall be permitted
to be used beyond the point of transition, a distance equal to
3.0 m (10 ft) or 10 percent of the circuit length figured at the
higher ampacity, whichever is less.
Pharon is offline   Reply With Quote
What is Code/Best Practices for Running a 240V cable to other Side of Room? imautoparts Electrical 16 01-02-2013 12:19 AM
Garage Insulation yamster Insulation 0 07-01-2011 01:30 PM
Installing insulation: side or face staple? deko Building & Construction 4 11-08-2010 12:17 AM
Romex Cable and fibreglass insulation fmva Electrical 4 11-13-2008 12:34 PM
Coaxial Cable Question bahaisamurai Home Theater 9 08-08-2007 02:54 PM