Securing A Wire Question - Electrical - DIY Chatroom Home Improvement Forum
Old 01-08-2010, 05:35 PM   #1
Rewards Points: 47
Question
Securing a wire question
Hello -
I've just ran Romex cable thru my metal conduit into a junction box. Do I need to/or how do I secure the cable inside of the metal box? The cable enters the box via an offset screw connector from the conduit.
Thanks.
dgates12 is offline   Reply With Quote
Old 01-08-2010, 05:38 PM   #2
Inspector/Instructor
codeone's Avatar
You need to secure the ground wire to the metal box with a green ground screw and then secure the NM(romex) within 12" of the top of the pipe.
You did put a protective plastic bushing at the top of the pipe didnt you?
codeone is offline   Reply With Quote
Old 01-08-2010, 05:40 PM   #3
Rewards Points: 47
...maybe that is what I forgot.
What does a plastic bushing look like?
Old 01-08-2010, 05:45 PM   #4
codeone's Avatar
This is one type you could use if you install a connector on the top end. They also make some push in ones. The bushing is not to secure the NM but to protect it from abrasion. The staple within 12" is to secure the NM.
Old 01-08-2010, 05:47 PM   #5
Rewards Points: 47
Cool
...thanks CodeOne! I'm off to Home Depot now to put these in. Good thing I haven't pulled the good wire thru yet, I just did a test with some spare stuff.
All you DIY readers rock! Thanks for all the help
Old 01-08-2010, 06:32 PM   #6
I am not 100% sure but I believe that you are NOT allowed to run romex in conduit.
paul100 is offline   Reply With Quote
Old 01-08-2010, 06:37 PM   #7
I was taught you are 100% correct!
Paelectrican is offline   Reply With Quote
Old 01-08-2010, 06:47 PM   #8
Rewards Points: 47
why couldn't I run romex in conduit? I've got 12/2 yellow indoor wire for the conduit in my attached indoor garage. What type of wire am I supposed to use?
Old 01-08-2010, 06:50 PM   #9
codeone's Avatar
Look in the 2008 NEC at code section 334.15(C).
In Unfinished Basements And Crawl Spaces.
"NM cable installed on the wall of an unfinished basementshall be permitted to be installed in a listed conduit or tubing or shall be protected in accordance with 300.4. Conduit or tubingshall be provided with a suitable insulating bushing or an adapter at the point the cable enters the raceway. The NM sheath shall extend through the conduit or tubing and into the device or outlet box not less than 1/4". The cable shall be secured within 12" of the point where the cable enters the conduit or tubing. Metal conduit, tubing, and metal outlet boxes shall be connected to an equipment grounding conductor."
Old 01-08-2010, 06:53 PM   #10
codeone's Avatar
Is your garage finished?
Old 01-08-2010, 06:53 PM   #11
Yup, NM in conduit is OK
The conduit has to be sized larger as the cable takes up more space then (3) THWN wires
12-2 is .1320 in size. 1 cable 1/2" is OK
Old 01-08-2010, 06:56 PM   #12
Is this code new for the 2008 edition of the NEC?
Old 01-08-2010, 06:58 PM   #13
codeone's Avatar
Also look at article 300.12(C) Exception
Exception No.1: Short sections of raceways used to provide
support or protection of cable assemblies from physical
damage shall not be required to be mechanically
continuous.
NM Is a cable Assembly
Old 01-08-2010, 06:59 PM   #14
codeone's Avatar
This is a new part for 2008.
However the second one I refered to is not.
300.12(C)Exception
Old 01-08-2010, 06:59 PM   #15
Well apparently my instructor was a little off when he told us that!! Thanks for the information.
Low Voltage Wire Shorting Rdakota06 Electrical 3 07-22-2009 01:15 PM
Dryer Grounding??? Traci_howdyadothat Electrical 7 05-27-2008 01:14 PM
3 wire to 4 wire question macmouse Electrical 24 05-01-2008 05:34 AM
Stranded wire on screw connections BigJimmy Electrical 7 01-19-2008 02:42 PM