Running Electric Underground - Electrical - DIY Chatroom Home Improvement Forum
Old 08-01-2010, 03:45 PM   #1
running electric underground
I am going to be running a new 50 amp electrical service from a house to a garage about 200 yards away. I am just inquiring about how the proper way to install the wire in the ground. I am unsure as to the depth, necessary conduit, how far down or above I need to have the warning tape and if I should be covering the conduit with anything (stone or concrete). Thanks for any help.
Seth
sethvel1 is offline   Reply With Quote
Old 08-01-2010, 04:14 PM   #2
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
well if youre going with direct burial wire id say trench it 30" to be safe,if your burying it in pvc pipe id say 24" should be plenty as long as you know where it is.
if youre going 200 yds underground in pipe id suggest 2"pvc to make it easier to pull,id also set a pull box or 2 somewhere along the line to make it easier
plummen is offline   Reply With Quote
Old 08-01-2010, 04:25 PM   #3
Thanks for the response. Yeah I was planning on the pull stations just not sure about the burial part. Thanks again.
Seth
Old 08-01-2010, 04:28 PM   #4
PVC pipe required depth is 18" to the top of the conduit
Unless you put concrete on top
Warning tape 12" over the conduit
With (3) #6 & a #10 ground you need 3/4" conduit to meet code
For that distance I would go with larger conduit....at least 1.5"
Actually need #4 wire to get voltage drop down under 3%
So with #4 & #8 ground you need 1" min, go at least 1.5" conduit
Old 08-01-2010, 04:56 PM   #5
plummen's Avatar
the thing that worries me about 18" to the top of a piece of pipe in that long of an open area is at some point if somebody comes along and grades it out your 18" can become 12" or less with one scoop of a bobcat bucket
Old 08-01-2010, 05:13 PM   #6
Thank you for the info Scuba Dave. Like Plumman said, I will probably go a little deeper than 18" just to be safe. I was planning on #4 wire too because of the run. Thanks again guys.
Seth
Old 08-01-2010, 05:23 PM   #7
Deeper is always better IMO
I went about 24" deep on my sub to the pool cabana
And about 30" deep on my new service feed
Old 08-01-2010, 09:02 PM   #8
Just what kind of loads are you going to have out there?
600 feet is a long ways away.
For a 3% voltage drop limit, the following wire sizes will give you:
#4 AWG = 20A @ 240V, or 4800 watts
#2 AWG = 30A @ 240V, or 7200 watts
#1 AWG = 40A @ 240V, or 9600 watts (slightly over at 3.2% drop)
For the full 50A @ 240V at max of 3% voltage drop, you would use 2/0, but you most likely will never use that much current out there.
Willis
williswires is offline   Reply With Quote
The Following User Says Thank You to williswires For This Useful Post:
Scuba_Dave (08-01-2010)
Old 08-01-2010, 09:09 PM   #9
Oh geez.....I saw the 200 & was thinking 200'
Yer gonna need some bigger wire
Measure that distance & be sure
Old 08-01-2010, 09:25 PM   #10
plummen's Avatar
thats why i suggested 2" pipe and pull boxes!
Old 08-01-2010, 09:39 PM   #11
" Euro " electrician
frenchelectrican's Avatar
50 amp size at 200 meter that is pretty good distance you will need at least 50mm˛ { 1 AWG } copper otherwise 55mm˛{1/0 AWG } alum will work good for this useage and yeah you will defentily need 2 inch PVC conduit that buried at least 24 inch deep or deeper.
Merci.
Marc
Old 08-03-2010, 04:45 AM   #12
My loads are only going to be 115 volt lights, garage opener and outlets. 50 Amps at 208V is over kill I'm sure, there will be no large loads or inrush. I didn't think I needed to go that large but I like to leave room for additions, especially after the work of that long of a run.
Old 08-03-2010, 07:11 PM   #13
plummen's Avatar
better to have too much,things change and it sucks to do twice
200 Amp or 400 Amp service Boontucky Electrical 37 07-24-2011 12:33 PM
Why is Inducer Fan Running? artbuc HVAC 3 07-31-2010 09:39 AM
String trimmers - gas, corded electric, or battery electric - which one?? whataboutj Landscaping & Lawn Care 43 05-01-2010 09:25 AM
Running Underground wiring to shop 200Ft kola Electrical 5 06-06-2008 09:13 AM
Running UF-B underground crash63 Electrical 7 04-26-2008 02:31 PM