Run Power To Remote Location Fo RV - Electrical - DIY Chatroom Home Improvement Forum
Old 01-17-2010, 02:17 PM   #1
Run power to remote location fo RV
I want to run 30A 110V power to a remote location on my property for an RV hookup 1,000' from my existing building, can this be done? I have 200A service in my existing building. Thanks, RH
h0mmeland is offline   Reply With Quote
Old 01-17-2010, 02:56 PM   #2
Do you know what the load will be at the RV with most things running ?
What will you be running for loads - devices ?
A 1000' run with 30a load = 28.6v drop with #6 wire (23.8%)
Woops...you are only running 120v...I calc'd for 240v
Corrected figures:
20a = 19.1v drop (15.9%), #4 would reduce that to 12 volts (10%), #3 reduces it to 9.5v (7.9%)
Maybe somebode else has an idea
Old 01-17-2010, 03:09 PM   #3
Rewards Points: 1,016
Will you be running the air conditioner? That is the biggest power draw device.
Old 01-17-2010, 03:13 PM   #4
MXer
3 legged dog's Avatar
30 amp, 1,000 Ft. That will take some large wire.
3 legged dog is offline   Reply With Quote
Old 01-17-2010, 03:23 PM   #5
I know it would take large wire; if I'm willing to bite the bullet and pay for necessary wire, what would be the right size if I did run the AC, and what would be the right size if I used NO AC, NO Microwave, NO Hairdryer, NO Coffemaker & NO toaster? Thanks to all of you guys! RH
Old 01-17-2010, 03:27 PM   #6
MXer
Acording to this http://www.csgnetwork.com/wiresizecalc.html 2/0.
Old 01-17-2010, 03:29 PM   #7
It all depends upon the loads
For a 30 Max load you would need 1/0 to bring it down to 7.1v & 5.9% drop
For a 20a load that reduces to 1 AWG & 5% voltage drop
For a 10a (1200w) load #4 would be a 5% drop
For just some lights a small 5a load (600w) #6 would be 4.8v & 4% drop
Old 01-17-2010, 03:31 PM   #8
1000' = relatives
Old 01-17-2010, 03:40 PM   #9
" Euro " electrician
frenchelectrican's Avatar
For 1,000 foot run there is two options it can be done however let me post two way it can be done with this kind of distance.
First option :
full 30 amp circuit @120 volts you will need 250 KCM for 3.1 voltage drop.
Second option :
Get two transfomers 120/480 volts { 3.5 Kw transfomer size each }
you can use #8 CU [ 2.4 % VD ] however this is a litte tricky if not addressed correct one of the secondary side { 480 } you have to ground one leg so you will get correct voltage referance.
{note I keep the voltage drop under 3% }
If you going this route let me know one of us will tell you the correct safe prodcure on this one this part is very important for safety issue espcally with this distance it involded.
Merci,Marc
Old 01-17-2010, 04:50 PM   #10
How often are you going to use the power at the RV - is a generator in some sort of a house a doable solution?