Recommendation For Exterior Run - Electrical - DIY Chatroom Home Improvement Forum
Like Tree6Likes
  • 1 Post By jbfan
  • 1 Post By Kwdelre
  • 1 Post By chandler48
  • 2 Post By rjniles
  • 1 Post By afjes2015
Old 11-02-2019, 12:41 PM   #1
Rewards Points: 20
Recommendation for exterior run
Hey folks,
I am running 210ft of 12/2 from a well pump to the main panel. What would be your preferred method?
1) Direct bury 12/2 wire ($117 at homedepot), save $100 on conduit
2) Use 12/2 wire ($117 at homedepot) run in $100 worth of 1" conduit
Play it safe with conduit and pull all that wire??
What do you think?
Kwdelre is offline   Reply With Quote
Old 11-02-2019, 03:39 PM   #2
Master Electrician
Rewards Points: 5,374
Re: Recommendation for exterior run
Either way you must dig a ditch. PVC conduit, 3 #10 conductors, two phase conductors and a grounding conductor.
brric is online now   Reply With Quote
Old 11-02-2019, 04:37 PM   #3
Rewards Points: 20
Thank you for the reply. Yep ditch is already dug.
The pump is a 3 wire 220v setup, but you recommend going to #10? I ask because the manual for the pump states that at 12AWG my max run can be 430ft @ 9% voltage drop. Shouldn't I be plenty good there? I am only going 210ft.
Thanks!
Old 11-02-2019, 05:29 PM   #4
Naildriver
chandler48's Avatar
Rewards Points: 3,528
Run individual THWN conductors sized depending on the pump rating. Run 4 wires. Red, Black, White and Green. The white will be capped off in the well house until such time you decide to install a light or heater or other 120 volt appliance. It also helps to add a receptacle to the well house for general use. Pulling cable is a PITA. You don't have to bury conduit as deep as you will UF cable, either. How deep is your ditch?
Larry......
Half of Communications is Listening, and You can't Listen with your Mouth.
chandler48 is offline   Reply With Quote
The Following User Says Thank You to chandler48 For This Useful Post:
Kwdelre (11-05-2019)
Old 11-05-2019, 02:14 PM   #5
Rewards Points: 20
So right now the ditch is 18-22" deep but I can go deeper.
The reason I was thinking of use the 12/2 (or 12/3 after your suggestion) is that it is much cheaper than the individual THWN. Plus wouldn't the individual wires cause me to need conduit?
Great call on the extra wire though....will definitely want a light at least.
Old 11-05-2019, 03:44 PM   #6
Electrical Contractor
jbfan's Avatar
Rewards Points: 6,770
Thanks!
I'm not sure if the manual is doing the VD correctly, but when figuring voltage drop, you use the from and the too distance.
If the distance in a straight line is 210', and means to the breaker, not just the ditch, you have the return distance also.
In this case the distance is 420'.
The best case is to use conduit and individual THWN wires, and I would do the #10.
Kwdelre likes this.
Yes I am a pirate, two hundred years too late
The cannons don't thunder, there's nothing to plunder
I'm an over-forty victim of fate.
The Following User Says Thank You to jbfan For This Useful Post:
Old 11-05-2019, 04:44 PM   #7
Naildriver
chandler48's Avatar
If you run UF cable the ditch will need to be 24". IMO, conduit and individual THWN wires are more stable and less likely to become compromised
Larry......
Old 11-05-2019, 06:56 PM   #8
Rewards Points: 20
You guys have given me some tough choices now, lol.
If I do the #10 THWN in conduit....can I do #14 ground? And what size conduit? Can I get away with 1" or am I asking for trouble. I have neevr pulled 200 ft before.
Am I good with THHN in conduit?
I like your signature by the way. (fellow parrothead)
jbfan likes this.
Old 11-05-2019, 06:59 PM   #9
Naildriver
chandler48's Avatar
Always think about the future. Running 1 1/2" conduit may be overkill for the moment, but you may see the need for an upgrade sometime out there, and with the larger conduit in place you can feasibly pull larger wires. I would go with a #12 ground. Generally it is one size smaller than the energized conductors.
Use pull string sucked through the conduit with a vacuum cleaner and a "rat" tied to the end of the string, then pull all the wires you need. Just don't do as my helper did. We were sending 250' of string from a 500' spool. He was not paying attention and wound up with 40' of string in the vacuum cleaner. He didn't hear the "thud".
Kwdelre likes this.
Larry......
Old 11-05-2019, 07:02 PM   #10
A "Handy Husband"
rjniles's Avatar
Rewards Points: 888
Full sized grounds required for #10, 12, 14
Sent from my Moto E (4) Plus using Tapatalk
chandler48 and Kwdelre like this.
My electrical answers are based on 2017 NEC, you may have local amendments.
The Following User Says Thank You to rjniles For This Useful Post:
Old 11-05-2019, 07:05 PM   #11
Rewards Points: 20
Thank you sir, looks like this is the way to go.
Old 11-05-2019, 09:33 PM   #12
Rewards Points: 20
All I can find around me is THHN...will this suffice?
Old 11-06-2019, 05:00 AM   #13
Naildriver
chandler48's Avatar
THHN and THWN are basically the same, sold often as THHN. THHN is Thermal High Heat Resistant Nylon. THWN adds the water resistant nomenclature.
Larry......
Old 11-06-2019, 06:02 AM   #14
Rewards Points: 760
Check at your local Home Depot or Lowers or the like in your area. The spool packaging usually only states THHN. Look closely at the printing on the insulation of the wire. You will see it is dual rated at THHN/THWN. Why they don't print it on the packaging I don't know.
jbfan likes this.
afjes2015 is offline   Reply With Quote