Receptacle And Plug Not The Same - Electrical - DIY Chatroom Home Improvement Forum
Old 08-25-2015, 05:05 AM   #1
Rewards Points: 2
receptacle and plug not the same
forgive my ignorance but I am in need of some assistance
I have a three prong female receptacle that reads 50A 125/250V, what I need is to plug in a three prong plug that reads 20A 250V.
is this a possibility? what do i need in order to accomplish this? any info will help my google-fu has been exhausted
receptacle and plug not the same-unnamed-1-.jpg   receptacle and plug not the same-unnamed.jpg
spooky-1 is offline   Reply With Quote
Old 08-25-2015, 05:43 AM   #2
Rewards Points: 129
The receptacle is a 240 volt receptacle with two hits and a ground . It doesn't matter what the plug days . That is just the maximum voltage that it is rated for . What we need its voltage rating if device that plug is connected two . It looks like a 20 amp plug for a 120volt device . One hot , one neutral and a ground . If that's the case you will need a new circuit . The dryer outlet won't work.
jimn01 is offline   Reply With Quote
Old 08-25-2015, 05:49 AM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,008
Wow. Care to try again?
Speedy Petey is online now   Reply With Quote
Old 08-25-2015, 05:52 AM   #4
Spooky, you cannot do what you propose.
You have an old non-grounding 50A 120/240V range receptacle. This is a 50A circuit with two hots, a neutral and no ground. This can only be used for a cooking appliance.
The plug is a NEMA 6-20, which is a straight 240V-20A plug, two hots and a ground. You need a 20A, 240V circuit to plug this in.
Old 08-25-2015, 06:10 AM   #5
dmxtothemax's Avatar
Rewards Points: 7,890
DITTO !
You cannot do it !
2 main reasons -
1 - you cannot plug a 20a into a 50s
BIG no no !
2 - said 50a outlet has no neutral.
So you need a new circuit.
dmxtothemax is offline   Reply With Quote
Old 08-25-2015, 07:04 AM   #6
Rewards Points: 3,396
the plug is 250v not 120 (no neutral)
op, there's something you can do, but you will need to do something. (sounds like something Yogi Berra would have said)
ritelec is offline   Reply With Quote
Old 08-25-2015, 07:07 AM   #7
what?
wouldn't be able to use that wire as a ground…? what?
It's probable a ground wire, and the exception to use it as a neutral was for the oven appliance.
Old 08-25-2015, 09:29 AM   #8
Rewards Points: 2,350
It is not a 240 volt receptacle. It is a 120/240 volt receptacle without a ground.
All is not lost of course, but it would require the neutral be moved in the panel to the ground bar, if it is a different bar, and the breaker be changed.
Old 08-25-2015, 10:50 AM   #9
Licensed electrician
Rewards Points: 4,548
Originally Posted by ritelec View Post
what?
Look at the terminal labels on a NEMA 10-50 receptacle. The straight slot is labeled W. It is not a ground.
Sometimes I would swear you were related to Cletus .
Speedy Petey (08-25-2015)
Old 08-25-2015, 11:01 AM   #10
yes I see it….. 125/250v
no ground…….
although it is……
it's neutral for sake of Current carrying, yet it is "grounded" ("ground" conductor) which goes to the chassis as "ground"……….. although it's neutral.
as mentioned, pretty sure it can be worked with………
AND, we are all assuming, who's to say there is any wire on that device..
and if there is who's to say it's not fed with 2 wire bx and maybe nothing is attached to the W………
there is a wire on the W who's to say it's going to the nutral and not ground..
we are assuming.
But yes………you are correct……… the receptacle configuration is 3 pole 3 wire, not 2 pole 3 wire grounding…
I like cletus..
Old 08-25-2015, 01:44 PM   #11
Rewards Points: 1,832
I do not see a ground on the 50amp range receptacle.
Jump-start is offline   Reply With Quote
Old 08-25-2015, 03:55 PM   #12
we are assuming.
And all these are simply silly assumptions. Possible sure, but really silly for you to even suggest all this nonsense.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Jim Port (08-25-2015)
Old 09-03-2015, 06:41 AM   #13
Rewards Points: 1,700
1- remove old 50A plug, put a 20a receptacle (with pigtails), use old neutral for ground.
2 - change panel breaker for double pole 20A. be sure the old neutral is now connected to ground bus.
carmusic is offline   Reply With Quote
New Range Hood - Replace Corded Plug or Install Receptacle Behind Chimney? Thadius856 Electrical 6 09-14-2012 04:35 PM
How to wire a receptacle to a male plug. ReefGuru Electrical 34 07-24-2012 10:39 AM
Help ID wallplate, plug, receptacle coultond Electrical 3 12-20-2011 08:32 PM
4prong dryer receptacle to 3 prong plug (6-15p to 14-30r) ChronPaul Electrical 11 11-26-2011 07:01 PM
wiring a light fixture to an existing plug receptacle box? San Mike Electrical 7 09-19-2011 12:58 PM