Prv Jumper Wire - Electrical - DIY Chatroom Home Improvement Forum
Old 10-07-2010, 11:35 AM   #1
47_47's Avatar
Rewards Points: 320
prv jumper wire
I just installed a water pressure reducing valve. Plumbing all copper and have 200 amp electrical service. What size jumper do I need? Do I need to connect the jumper back to ground rod, to the panel, existing one at the water meter or can it just be connected to the inlet and outlet piping of the prv?
Thanks,
Mike
47_47 is offline   Reply With Quote
Old 10-07-2010, 11:53 AM   #2
Just call me Andrew
Rewards Points: 1,032
Is the PRV right next to the meter? If so you can probably use one large jumper to go over both devices. One end on the inlet from the street (before the meter), the other end downstream of the PRV. This would save some money as you would not need to buy additional pipe clamps (about 5 bucks each).
I think you need a #6 green or bare jumper for 200A service.
Jumper wires do not need to go back to the panel or ground rods. The only point of them is to bridge the connection if a device is removed for service.
Andrew
secutanudu is offline   Reply With Quote
Old 10-07-2010, 12:24 PM   #3
47_47's Avatar
Rewards Points: 320
The prv is about 7 feet away and the existing wire to the meter will not reach. As long as I can just jumper the prv, I'll get two feet of #6 bare and a couple of clamps. Thanks
Old 10-07-2010, 12:26 PM   #4
Rewards Points: 320
I might be mistaken but I think that 200 amps requires a #4 wire.
teamo is offline   Reply With Quote
Old 10-07-2010, 12:37 PM   #5
Rewards Points: 320
I was mistaken it is #6.
The Following User Says Thank You to teamo For This Useful Post:
47_47 (10-07-2010)
Old 10-07-2010, 01:44 PM   #6
Licensed electrician
Rewards Points: 3,654
A #4 would be required on the water line jumper.
Old 10-07-2010, 02:03 PM   #7
47_47's Avatar
Rewards Points: 320
Thank you, Jim. Just out of curiosity how did you determine I need #4?
Old 10-07-2010, 02:09 PM   #8
Just call me Andrew
I used this chart....so I am curious as to why it is #4 also. Maybe there are specific rules regarding water pipe bonding?
Andrew
Old 10-07-2010, 02:44 PM   #9
Use Table 250.66, not 250.122. Grounding electrode conductor are not sized the same as equipment grounding conductors.
secutanudu (10-07-2010)
What type wire to use from transfer switch to outdoor outlet brjl Electrical 32 11-20-2013 08:36 AM
Proper Use of Green Wire Nuts HooKooDooKu Electrical 16 06-29-2012 06:41 PM
HALP! Master/Remote Dimmer troubles! Confuserated Electrical 9 02-12-2010 03:30 PM
Decommissioning old armored wire circuit toddmanqa Electrical 6 12-04-2009 08:55 AM
Burial wire and a seeming difference of opinion... SxS Electrical 19 02-24-2009 09:16 AM