Problem With Breakers In Panel Box - Electrical - DIY Chatroom Home Improvement Forum
Old 03-19-2010, 04:30 PM   #1
Problem with breakers in panel box
My 7,11 and 15 breakers in the shop are working fine, but the 5,9 and 13 breakers on the same side are not working. This shop is fed from a 60amp breaker from my house to a 60amp breaker in the shop on the right side of the panel. What is the problem?
fishersd327 is offline   Reply With Quote
Old 03-19-2010, 04:34 PM   #2
Master Electrician
Rewards Points: 5,082
Assuming they're full size breakers and not tandems it sounds as if you've lost a leg of your feed. Are all of the even numbered breakers fully functional?
brric is online now   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
fishersd327 (03-19-2010)
Old 03-19-2010, 04:52 PM   #3
The 5-13 breakers are all 20amp Cutler-Hammer breakers. Only thing on even side is the than 60amp main breaker
Old 03-19-2010, 05:43 PM   #4
Licensed Pro
Like brric said, you have lost one hot leg to the panel. Do you have any way to test for voltage (meter, test light)?
Old 03-19-2010, 06:02 PM   #5
Master Electrician
SD515's Avatar
Rewards Points: 506
You've lost power to the left busbar of the panel. Try resetting both 60A breakers. If 5, 9 & 13 come back alive, investigate as to what could have caused the 'leg' to be lost.
Kyle
Old 03-19-2010, 06:05 PM   #6
Is this a new sub or it was working & suddenly stopped ?
Shut power off to the sub & tighten down the hot feeds
Check the breaker in the main panel & make sure hots are secure
Main Panel / Service Upgrades gbe Electrical 12 11-06-2009 11:20 PM
100 -> 200 amp panel upgrade questions philipjcaputo Electrical 1 10-30-2009 03:35 AM
Passing wire to another panel theatretch85 Electrical 5 09-20-2009 11:09 PM
Moving several circuits to sub panel WoodworkerDave Electrical 2 09-27-2008 02:05 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM