Practical Considerations For UF - Electrical - DIY Chatroom Home Improvement Forum
Old 03-08-2015, 12:56 AM   #1
Restoration professional
Rewards Points: 302
Practical considerations for UF
I have UF wire running to my detached garage. On the house side, it enters metal conduit at the point it leaves the dirt, then connects to breaker box. The end of the metal conduit is simply cut off a couple inches below the dirt. Is this how it's supposed to be?
halliwellc is offline   Reply With Quote
Old 03-08-2015, 01:12 AM   #2
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
no. Being cut off isn't the problem. Being cut off so close to the surface is the problem. It needs to be protected by conduit any time it is less than 24" below the surface.
I also prefer to install a push on plastic bushing to make sure the conduit cannot cut the wire.
Old 03-08-2015, 07:04 AM   #3
Rewards Points: 455
Metal conduit should not float above ground with live conducts within. Often times conduit of some sort is used for protection of the wires or cable against physical damage. Non metallic is best for that, but if metal conduit is used it has to be bonded. So I see that as a problem here also.
sparky90 is offline   Reply With Quote
Old 03-08-2015, 08:17 AM   #4
Master Electrician
Rewards Points: 5,248
NEC reference please.
brric is offline   Reply With Quote
Old 03-08-2015, 08:21 AM   #5
Licensed electrician
Rewards Points: 3,736
The OP says the conduit connects to the panel so it is already bonded.
Old 03-08-2015, 11:05 AM   #6
Rewards Points: 455
Not bonding in this situation may be OK under an exception of it being used as a wire protection. Guess its OK then. If it gets energized it could be a problem though. Hopefully it won't.
Old 03-08-2015, 02:06 PM   #7
nap
You talking to me?
nap's Avatar
a correction to my input:
the protection is only required to extend to no less than 18" below grade per 300.5(D)(1)
also, per 300.5(D)(4) if the raceway (conduit) is subject to damage (like in where a lawnmower might throw sticks or stones and hit it) RMC, IMC, schedule 80 pvc or equivalent must be used.
and a bushing MUST be used (per 300.5(H))
and with brric's prompting:
per 300.10 exc 1; short sections of raceways used to provide support or protection of cable assemblies from physical damage shall not be required to be made electrically continuous.
The Following 2 Users Say Thank You to nap For This Useful Post:
brric (03-08-2015), Vegas Sparky (03-08-2015)
Is opening the ceiling and upstairs floor practical? papernpaste Building & Construction 4 12-06-2014 01:07 PM
considerations for refinishing grooved wood floor? rasz Flooring 8 09-04-2011 06:32 AM
Any practical way to remove a hedge fence? Beginner here jamesrwrightiii Landscaping & Lawn Care 19 10-07-2009 06:50 PM
What is the heaviest and longest hand auger that is practical? darsunt Plumbing 1 08-17-2009 10:29 PM