Oversize Wire - Electrical - DIY Chatroom Home Improvement Forum
Old 02-09-2010, 09:59 AM   #1
oversize wire
is it ok to oversize wire? I have 6 guage wire that I am using for a 30 amp breaker. I guess should have bought #8. The breaker says #8 to #14 on the side of it. Thanks
daddyrabbit is offline   Reply With Quote
Old 02-09-2010, 10:21 AM   #2
Rewards Points: 308
Technically no. Only because the breaker says no. In reality, if the wire will fit comfortably into the breaker screw terminal it will be just fine.
I would use it with no reservations at all.
Old 02-09-2010, 03:13 PM   #3
Idiot Emeritus
Rewards Points: 80
you could also splice a short piece of #10 (or #8) onto the #6, and land the #10 on the breaker.
Splices are OK in a panel.
Rob
micromind is offline   Reply With Quote
Old 02-09-2010, 07:33 PM   #4
Rewards Points: 35
Unhappy
Oversize wire
Things are never as simple as we think they should be. NEC 250-122 tells us that if the current carrying conductors are sized up, the ground must also be sized up by the same percentage. This means that instead of using a #10 ground wire, it will have to be larger.
czars is offline   Reply With Quote
Old 02-09-2010, 08:28 PM   #5
thanks. I have all 4 wires #6. I bought them thinking I was going to upgrade to 50 amp on that circuit in the future. I might just bite the bullet and buy some #8 wire and save the #6's for another project down the road
Old 02-09-2010, 08:36 PM   #6
Rewards Points: 1,016
If you think you may install the 50 amp in the future, go ahead an use the #6. Nothing wrong with doing it as outlined by others.
Old 02-11-2010, 12:24 PM   #7
Rewards Points: 308
Sure they are. Article Table 250.122 tells us that a #10 is required for the 30 amp breaker. #10 is good all the way up to a 60 amp breaker. The ground (EGC) is sized according to the OCPD not the size of the other wires.
Old 02-11-2010, 12:59 PM   #8
Electrical Contractor
kbsparky's Avatar
The problem here is if you use a #6 wire on a 30 Amp breaker, you are required to use a #6 EGC. I don't agree with it either, but that is the Code for ya. See 250.122(B).
-KB
Adding a wall switch to a pull chain fixture abacuslearns Electrical 17 12-20-2011 06:02 PM
Red wire is HOT genner Electrical 15 02-22-2009 08:14 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
Stranded wire on screw connections BigJimmy Electrical 7 01-19-2008 02:42 PM
Stove Top wire capt2 Electrical 8 10-05-2007 01:41 PM