Outlet Codes On A Kitchen Peninsula - Electrical - DIY Chatroom Home Improvement Forum
Old 03-06-2012, 07:15 AM   #1
outlet codes on a kitchen peninsula
my peninsula has no back wall to put an outlet .. my last outlet is 5 feet from end ... is one required
byronkirby65 is offline   Reply With Quote
Old 03-06-2012, 07:28 AM   #2
Super Moderator
joed's Avatar
Rewards Points: 31,596
Post your location. It makes a difference.
The Following User Says Thank You to joed For This Useful Post:
Code05 (03-06-2012)
Old 03-06-2012, 07:47 AM   #3
Code05's Avatar
Rewards Points: 1,104
If you are in USA, you need a receptacle.
(2) Island Countertop Spaces. At least one receptacle
shall be installed at each island countertop space with a
long dimension of 600 mm (24 in.) or greater and a short
dimension of 300 mm (12 in.) or greater.
(3) Peninsular Countertop Spaces. At least one receptacle
outlet shall be installed at each peninsular countertop
space with a long dimension of 600 mm (24 in.) or greater and
a short dimension of 300 mm (12 in.) or greater. A peninsular
countertop is measured from the connecting edge.
(4) Separate Spaces. Countertop spaces separated by
rangetops, refrigerators, or sinks shall be considered as
separate countertop spaces in applying the requirements of
210.52(C)(1). If a range, counter-mounted cooking unit, or
sink is installed in an island or peninsular countertop and
the depth of the countertop behind the range, countermounted
cooking unit, or sink is less than 300 mm (12 in.),
the range, counter-mounted cooking unit, or sink shall be
considered to divide the countertop space into two separate
countertop spaces. Each separate countertop space shall
comply with the applicable requirements in 210.52(C).
It may be installed in the pennisula if conditions allow.
Exception to (5): To comply with the conditions specified in
(1) or (2), receptacle outlets shall be permitted to be
mounted not more than 300 mm (12 in.) below the countertop.
Receptacles mounted below a countertop in accordance
with this exception shall not be located where the
countertop extends more than 150 mm (6 in.) beyond its
support base.
Code05 is offline   Reply With Quote
Changing Two Gang Outlet to Three Gang Outlet vbullinger Electrical 9 01-10-2011 05:13 PM
kitchen design: should we remove inner wall(s)? ilyaz Kitchen & Bath Remodeling 4 10-26-2010 07:59 AM
Kitchen Sink Moved - new kitchen sleepysmurf Plumbing 1 08-10-2010 06:38 AM
outlet in peninsula aaojane Electrical 2 06-23-2010 12:15 PM
Idea for kitchen peninsula acomiskey Remodeling 3 05-17-2008 02:12 PM