Outdoor Receptacles - Electrical - DIY Chatroom Home Improvement Forum
Old 06-05-2010, 12:26 PM   #1
Outdoor Receptacles
I would like to extend power from my outside main power panel to 3 or 4 receptacle that would line the outside of my concrete pool deck. The power line would run through a rock bed that rarely has any foot traffic.
Am I required to bury the conduit that would carry the power cable? Can I lay down PVC pipe or Liquid Tight? Each outlet receptacle would be mounted on a pole 1ft above ground.
tks for your help.
usnavy1610 is offline   Reply With Quote
Old 06-05-2010, 09:42 PM   #2
Electrical Contractor
kbsparky's Avatar
Those outlets would be required to be at least 10 feet (3 m) away from the pool. They would also be required to be wired in conduit.
-KB
Old 06-05-2010, 10:00 PM   #3
680 covers pools
680.22 at least 6' from the inner wall of the pool
10' if for the pool pump, but there are exceptions for pump that allows within 6' - must meet all: single receptacle, locking, grounding & have GFCI
So you can install them as long as they are not closer then 6'
You want to run the conduit along the ground instead of burying it ?
Is there a wall or something that it will be secured to ?
Not sure on running along the ground
Old 06-05-2010, 11:09 PM   #4
Rewards Points: 506
any stray foot pressure on a rock covered conduit could place your entire weight on one small spot of conduit, breaking it.
forresth is offline   Reply With Quote