Open ground gfci?
There are 3 gfci above kitchen countertop. 2 record as fine but one is recording open ground, what could do that?
Mikeron is offline   Reply With Quote
Old 10-20-2015, 01:18 PM   #2
Rewards Points: 2,084
A ground wire that is not connected to the outlet. Open it up.
John Grabowski
MrElectrician.TV
MrElectricianTV is offline   Reply With Quote
Old 10-20-2015, 01:43 PM   #3
Rewards Points: 294
This just has two wires a red and white, same runs in the junction box.
Should I take it out and replace with new 12/2 romex?
Old 10-20-2015, 02:05 PM   #4
Rewards Points: 516
It's GFCI'd so put a label on the receptacle that says "no equipment grounding conductor "
Arrow3030 is offline   Reply With Quote
Old 10-20-2015, 02:09 PM   #5
A "Handy Husband"
rjniles's Avatar
Rewards Points: 796
only having RED AND WHITE is unusual. Are the wires in conduit?
My electrical answers are based on 2017 NEC, you may have local amendments.
rjniles is offline   Reply With Quote
Old 10-20-2015, 04:06 PM   #6
Rewards Points: 18,784
And having three GFI's is strange.
Location may help. In the US you need two 20 Amp. GFI protected circuits over a counter.
Only one GFI is needed per circuit.
Old 10-20-2015, 05:40 PM   #7
Rewards Points: 3,278
Multiwire branch circuits usually have a red wire.
MWBCs usually require a separate ground fault circuit interrupter receptacle at each outlet location if a GFCI 2 pole breaker was not used.
Unlike when dealing with the neutral, there are no special tricks needed to run the equipment grounding conductor to the various receptacles in a daisy chained MWBC.
Stop some of your bank autopayments so you can set priorities for manual monthly payments out of your coronavirus stimulus check.
AllanJ is online now   Reply With Quote
Gfci - no ground SPS-1 Electrical 1 06-29-2015 07:59 PM
Open Ground... JohnC20 Electrical 9 07-20-2013 06:47 PM
2 Similar GFCI, but one tests open ground crescere Electrical 40 08-28-2012 09:19 PM
Open Ground in Non Daisy Chained Outlet Circuit RileyRR Electrical 2 05-18-2011 02:00 PM
Help Needed with Open Ground mark2741 Electrical 35 08-29-2010 03:10 PM