One Neutral For Multiple Hits? - Electrical - DIY Chatroom Home Improvement Forum
Like Tree1Likes
  • 1 Post By Speedy Petey
Old 08-15-2016, 10:23 AM   #1
Rewards Points: 74
One neutral for multiple hits?
More of a just curious question but I've seen conduit with one neutral and 3 or 4 different hots for different circuits. When pulling wire in conduit do you only have to have one neutral for multiple circuits? Or should each circuit have its own neutral pulled back to the panel? Don't deal with conduit much but Iight add some circuits to my garage and was thinking about using conduit surface mounted so just setting I got to thinking about last night. Say I wanted to add 3 or 4 outlets each on their own breaker. Can I just run 4 hots and one neutral or do I need a separate neutral for each circuit like romex has?
ponch37300 is offline   Reply With Quote
Old 08-15-2016, 10:38 AM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 312
Re: One neutral for multiple hits?
You need a separate neutral for each circuit. You could run 2 MWBCs. From a 2 pole breaker run 2 hots, 1 neutral for each circuit
That will give you 4 dedicated receptacles. You only need 1 ground or use the metal conduit as ground. The receptacles must be GFCI protected.
My electrical answers are based on 2014 NEC, you may have local amendments.
The Following User Says Thank You to rjniles For This Useful Post:
Jim Port (08-15-2016)
Old 08-15-2016, 02:16 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,006
Keep in mind that most new circuits in a dwelling now require AFCI protection, so running MWBCs (shared neutral circuits) is not the best idea. Two-pole AFCI breakers are not widely available yet, and not for all panels.
Jim Port likes this.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Knows a Little (08-16-2016)
Old 08-15-2016, 03:17 PM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 312
Petey, the poster says the 4 new circuits are for the garage.The 2014 NEC does not require AFCI for garages (YET). Also He is in Wisconsin which apparently is on 2011
Old 08-15-2016, 06:03 PM   #5
Ah! Missed that, thanks.
Old 08-15-2016, 07:35 PM   #6
Rewards Points: 3,002
You should not have seen 4 hot wires and one neutral.
But in a commercial or industrial building it is common to have 3 phase feeds and branch circuits and these have 3 hots and one (sometimes no) neutral.
Stop some of your bank autopayments so you can set priorities for manual monthly payments out of your coronavirus stimulus check.
AllanJ is online now   Reply With Quote
The Following User Says Thank You to AllanJ For This Useful Post:
Old 08-16-2016, 04:47 PM   #7
Correction: We can have numerous hot conductors all sharing the same neutral in a conduit where some of those hot conductors are controlled by upstream switches
Old 08-18-2016, 10:55 PM   #8
Rewards Points: 382
They do all have to be on the same breaker. You can't pair hots from one circuit with neutrals from another. If you do that, you risk overloading the neutral. It's not clear to me if the OP has that situation or not.
fa_f3_20 is offline   Reply With Quote
Generator & Interlock Kit Float the Neutral? Arnold Ziffel Electrical 12 01-13-2013 05:28 PM
Unused ground lead as neutral? ramatsu Electrical 13 01-10-2012 07:44 PM
Need Neutral Connections - Installing Subpanel ctlu008 Electrical 10 01-01-2012 07:54 AM
Will reverse polarity trip breaker?? Duane 70 Electrical 60 12-05-2008 10:18 PM
Suspected open/loose service neutral mrtomwj Electrical 5 09-28-2006 08:46 AM