Re: Old Zinsco Service Panel - No ground?
Originally Posted by Jim Port View Post
Check for continuity from the neutral to the case.
Quick question, I didn't have a chance to check yet as I'll have to go pick up a multimeter. My current tester doesn't have a continuity option.
If continuity exists between the neutral bar and the case, does this mean that I can connect my ground wire from UF-B to the neutral bar?
818han is offline   Reply With Quote
Old 08-25-2018, 05:32 PM   #17
Rewards Points: 800
Originally Posted by joed View Post
I don't see any ground wires in that panel anywhere. I do see a white cable that appears to be bolted to the chassis under the two red wires.
Yes, I am seeing the same situation. The # 6 copper white conductor (?) (yellow dash lines) is mechanical lugged down to the back of the breaker box cabinet right under the two red wires. (small yellow circle) Then, it short jumpers over and enters a bonding lug on a metallic grounding bushing (larger yellow circle) on what appears to be maybe a 3/4" metal conduit fitting ??
Gregsoldtruck79 is offline   Reply With Quote
Old 08-25-2018, 07:33 PM   #18
Rewards Points: 26
I'm going to go take a look at the panel again in about an hour. Assuming that you're correct, does this indicate the metal casing of the panel is grounded? If so does that make the neutral bar grounded? Nonetheless I'll run a continuity test.
Old 08-25-2018, 08:40 PM   #19
Rewards Points: 800
Not necessarily. But if I am right, someone was assuming by installing a white conductor with a lug to the breaker box sheet metal back, and then ran it to the conduit fitting's grounding bushing lug...they were "bonding" the two and grounding them. This action does not assure the breaker box is grounded though, it just implies so... until it is proven to be or not.
Old 08-26-2018, 05:29 PM   #20
Rewards Points: 26
So what is interesting is I tested positive for continuity between the white conductor/grounding bushing lug and the neutral bar. I assume this means the neutral bar is indeed grounded?
Old 08-26-2018, 06:00 PM   #21
Licensed electrician
Rewards Points: 3,594
The incoming white connects to the neutral bar for the branch circuits. It does not mean you panel is bonded. You need to go between the case and the neutral bar.
Old 08-26-2018, 07:33 PM   #22
Rewards Points: 26
Hmm not getting continuity when testing between the case and the neutral bar. I am getting it when testing between the neutral bar and the grounding bushing (large circle) that Greg identified. The wire from the grounding bushing is bolted to the panel (smaller circle)
Old 08-26-2018, 08:07 PM   #23
Rewards Points: 26
UPDATE: I went ahead and cleaned up the debris and paint from the case with a flat head in multiple spots. After doing so, I tested continuity between the neutral bus and the case in those spots.
All tested positive for continuity.
Main Service panel grounding question KirkJT Electrical 17 05-25-2016 03:35 PM
Wire 200A Subpanel that will become main panel NickWa Electrical 7 02-19-2015 01:55 PM
Need help installing new service and making old service a sub panel fightermage Electrical 9 09-26-2012 08:48 PM
Moving service panel away from main service line entry k2000lbs Electrical 3 11-28-2011 08:39 AM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM