Nuetral Wire Size - Electrical - DIY Chatroom Home Improvement Forum
Old 03-04-2018, 10:21 PM   #1
Rewards Points: 2
Nuetral Wire size
For my personal education, please explain the difference in these two MHF cables (mainly the difference in the neutral and ground sizes and why each variation is produced).
2/0-2/0-2/0-1
2/0-2/0-1-4
Under what cirumstances is the larger neutral required?
Installing in U/G conduit going 300 feet from 200 (240v) amp main to 100 amp sub in shop. Basic power tools, lights small air compressor maybe a small fridge. Will almost certainly never run the full 100 amps.
Do I have to have the 2/0 neutral or can I use the 1 gauge?
10022089 is offline   Reply With Quote
Old 03-04-2018, 10:30 PM   #2
Master Electrician
Rewards Points: 5,384
Re: Nuetral Wire size
What is MHF cable?
brric is online now   Reply With Quote
Old 03-04-2018, 10:34 PM   #3
Rewards Points: 2
Mobile home feeder
Old 03-04-2018, 10:39 PM   #4
Master Electrician
Neither one is adequate for 100 amps unless the conductors are copper.
Old 03-04-2018, 11:21 PM   #5
mr_robot's Avatar
Rewards Points: 16
Huh? 2/0 AL or CO are both major overkill for 100a. It's rated at 135a for AL and 175 for CO.
Why are you using mobile home feeder cable? Why not just run individual XHHW-2 wires in the conduit? Why pay for the extra expense of a cable assembly? Or if you use direct burial cable, then why run the conduit continuous underground? You only need to sleeve it as it emerges from grade to the minimum burial depth of 24".
For 100a you need #3 CO or #1 AL and a #8 CO or #6 AL ground.
Also be sure to install a separate ground bar in the sub panel and do not bond the neutral to the enclosure with the green screw or copper bonding strip. You also need to install a supplementary ground rod with #6 CO and terminate it on the ground bar because it is a separate building.
Sent from my A574BL using Tapatalk
mr_robot is offline   Reply With Quote
Old 03-04-2018, 11:24 PM   #6
mr_robot's Avatar
Rewards Points: 16
You need to use a full size neutral. The MHF has a version with a smaller neutral because it is meant to serve an entire dwelling unit where it is sometimes possible to reduce the neutral size. This is not the case with your outbuilding.
Old 03-04-2018, 11:27 PM   #7
mr_robot's Avatar
Rewards Points: 16
I just now noticed that your run is 300 feet. Did you oversized this cable to compensate for voltage drop? Or did you just not know what size cable you needed? Regardless it would be a good idea to oversize the cable for such a long run.
Old 03-05-2018, 06:43 AM   #8
Rewards Points: 2
I had an engineer from electric company come out and see about setting a new pole down by the shop. He's the one who suggested the mobile home feeder wire in lieu of a new pole because I have the 200 amp main and currently only run 75 amps at peak. Using the online calculators, It seems like the 2/0 is borderline on the wrong side with the voltage drop at 300 feet. I figure 4/0 would be best but would rather avoid the added troubles of the 4/0 if I can.
Old 03-05-2018, 07:15 AM   #9
Master Electrician
You are correct. I misread the post as 2/2/2. My bad.
Old 03-05-2018, 07:18 AM   #10
Master Electrician
Be advised, 4/0 conductors will need to be reduced in size at the termination points as they will not fit into a 100 amp breaker.
Old 03-05-2018, 07:24 AM   #11
Rewards Points: 2
yea that's one of the troubles I'm hoping to avoid by using the 2/0. So will the 2/0 be ok and I have to use th 2/0 neutral as well?
Old 03-05-2018, 07:29 AM   #12
Very Stable Genius
CodeMatters's Avatar
Rewards Points: 8,136
If you made the feed breaker 80A's then 2/0 AL would be fine with 300' run.
Still plenty of power for what you want to do.
Wouldn't suggest reduced neutral.
CodeMatters is offline   Reply With Quote
Old 03-05-2018, 10:32 AM   #13
mr_robot's Avatar
Rewards Points: 16
4/0 is overkill. 2/0 would work fine. You'd have to order an 80a breaker from a supply house as they are not available at home depot, Lowe's, etc.
I would just use a 100a breaker. The breaker has nothing to do with voltage drop. It's the actual connected load that makes the difference.
The neutral needs to be the same size as the ungrounded conductors unless you can show that you have a reduced neutral load, perhaps due to a majority of 240v equipment, but why bother? I am not a fan of reducing neutrals simply because of the levels of harmonic currents in modern equipment and electronics.
Tags
240 volt , amp , conduit , neutral , sub panel
Digitial Timer in 3 Gang box with (2) 3way switches and 1 single pole..confused. BCS Electrical 33 03-20-2016 11:30 PM
New Sub Panel Wire Size? johnsas Electrical 4 08-29-2012 11:20 AM
Ground Location and Wire Size LHB_Texas Electrical 25 05-27-2011 09:38 AM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 05:00 PM