No Power To Any Outlets In Garage - Electrical - DIY Chatroom Home Improvement Forum
Old 04-26-2016, 12:24 PM   #1
Rewards Points: 2
no power to any outlets in garage
Good breaker. all outlets read 120 volts form white to ground and black to ground. from white to black zero voltage. pull all outlets. no joy
wapayne is offline   Reply With Quote
Old 04-26-2016, 12:33 PM   #2
Jello Wrangler
Rewards Points: 539
Re: no power to any outlets in garage
How would you get 120 volts from white to ground?
ChiTownPro is offline   Reply With Quote
Old 04-26-2016, 12:45 PM   #3
Rewards Points: 114
Does any of this help?
http://www.diychatroom.com/f18/why-1...uetral-137093/
Phases is offline   Reply With Quote
Old 04-26-2016, 02:15 PM   #4
Oso954's Avatar
Rewards Points: 1,814
The short answer is an open neutral and some load that is plugged in or switched on.
Voltage (potential) passes thru the load, but the load does not operate because there is no current flow.
Oso954 is offline   Reply With Quote
The Following User Says Thank You to Oso954 For This Useful Post:
Jim Port (04-26-2016)
Old 04-26-2016, 03:01 PM   #5
Super Moderator
joed's Avatar
Rewards Points: 31,914
Open neutral. No doubt in mind.
If the garage is detached the buried cable could be damaged.
Old 04-26-2016, 03:25 PM   #6
Jello Wrangler
Rewards Points: 539
How do you figure? There is no voltage on the neutral to hot. But voltage on H-G and N-G.
Old 04-26-2016, 03:36 PM   #7
Oso954's Avatar
Your meter reads the differance between the 2 probes. So with 120v of the same leg on the hot and the neutral, the difference is zero.
Yet each reads 120v to ground.
Old 04-26-2016, 05:27 PM   #8
Super Moderator
joed's Avatar
The voltage on the neutral is being fed through some device on the circuit. The circuit is not complete because the neutral is open between the test point and the panel.
Old 04-26-2016, 09:26 PM   #9
Jello Wrangler
Rewards Points: 539
That doens't explain why the hot is dead or why he's ready 120 on the neutral. If it's being fed from another device it should be lower than 120.
Old 04-26-2016, 09:37 PM   #10
A "Handy Husband"
rjniles's Avatar
Rewards Points: 882
The full voltage is read thru the load on the neutral because without a closed circuit there is no voltage drop.
My electrical answers are based on 2017 NEC, you may have local amendments.
Old 04-26-2016, 10:01 PM   #11
Super Moderator
joed's Avatar
You don't understand how electricity works. It is not being fed from another device. The voltage is passing through a device on the circuit.
Old 04-26-2016, 11:20 PM   #12
Jello Wrangler
Rewards Points: 539
I do, it's symatics "fed" "passing through", whatever. The fact is even if it passes through a device it will have some voltage drop. Both will not read 120v. In fact it's suspect that it's reading 120. Most often it will read between 116v-118v.
Old 04-27-2016, 02:44 PM   #13
Super Moderator
joed's Avatar
Please explain how there can a voltage drop if there is NO current flow.
The Following 2 Users Say Thank You to joed For This Useful Post:
Oso954 (04-27-2016), rjniles (04-27-2016)
Old 04-27-2016, 04:41 PM   #14
randyhenke's Avatar
At your breaker do you have 120v to ground? Are your lights on the same circuit breaker and do any of them work? Is anything operational on that circuit? Last thing make sure you don't have a disconnect somewhere that is wired incorrectly (switched nuetral) that you may have overlooked.
Check for an open nuetral. You shouldn't have more than a volt or two max between ground and nuetral. You should really see only a few millivolts. I'd suspect the breaker then the first device that feeds power since none of your outlets work. I would be checking all connections are tight.
Sent from my XT1097 using Tapatalk
randyhenke is offline   Reply With Quote
detached garage has no power yellowtail Electrical 56 02-27-2014 10:38 AM
No Power to Outlets in Garage rs1971 Electrical 7 02-02-2013 11:06 PM
Lights turn on. No power to wall outlets StarStryker11 Electrical 4 01-01-2013 04:25 PM
Wiring for switched, split power outlets ELurie Electrical 9 06-21-2007 07:12 PM