No Ground In Garage - Electrical - DIY Chatroom Home Improvement Forum
Old 04-27-2016, 01:54 PM   #1
Rewards Points: 20
No ground in garage
In the process of restoring power to my garage dealt with in another thread, I discovered that there is no ground connection back to the house panel. The previous owner had run a two conductor UF cable without a ground wire.
Can I install a ground rod next to the garage foundation and hook to that? Or do I have to run a complete new cable from the house panel to the garage. The cable would have to go under a sidewalk, so I'd rather not go that route if there's a safe alternative.
Bythepond88 is offline   Reply With Quote
Old 04-27-2016, 02:40 PM   #2
Licensed electrician
Rewards Points: 3,872
Re: No ground in garage
How much capacity do you need at the shed? Do you need any 240 volt loads? Is there any metallic path back to the house?
Old 04-27-2016, 03:54 PM   #3
Rewards Points: 20
No, I do not need any 240v load. I will just be running a light over the bench, the garage door opener, and the occasional hand power tool, and maybe a planer for short periods from time to time. (Not all at once, of course.)
Old 04-27-2016, 04:01 PM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 904
There is no approved way correct this without running a new cable.
If you wish to continue using what you have, add a GFCI receptacle at the first appearance of the UF cable and feed the rest of the garage off the load terminals.
My electrical answers are based on 2017 NEC, you may have local amendments.
Old 04-27-2016, 05:13 PM   #5
Rewards Points: 516
A ground rod in this scenario would be more likely to shock someone than open a circuit breaker. Electricity isn't trying to go to earth. GFCI protection is the best option besides running a new cable.
Arrow3030 is offline   Reply With Quote
The Following User Says Thank You to Arrow3030 For This Useful Post:
mm11 (04-28-2016)
Old 04-27-2016, 05:59 PM   #6
Rewards Points: 20
Can I install a GFCI without a separate ground wire?
Old 04-27-2016, 06:16 PM   #7
A "Handy Husband"
rjniles's Avatar
Rewards Points: 904
GFCI does not require a ground to operate. It senses an unbalance between the hot and neutral.
Old 04-27-2016, 06:37 PM   #8
Rewards Points: 20
Thanks for the advice. I'll go with a GFCI, then.
Old 04-27-2016, 08:23 PM   #9
Rewards Points: 774
Actually what he has is basically a separate service much like what the utility runs to any residence except in lieu of 240/120 3 wire he has 120 2 wire. He can and most likely should install a circuit breaker panel and drive a ground rod grounding the neutral. He should still utilize the GFCI.
Know A Little is offline   Reply With Quote
The Following 2 Users Say Thank You to Know A Little For This Useful Post:
ChiTownPro (04-28-2016), mpoulton (04-29-2016)
Old 04-27-2016, 08:27 PM   #10
Rewards Points: 774
DIY would not let me use the EDIT feature for some reason.
Can you explain how you think a ground rod could make this installation more of a shock hazard?
Old 04-27-2016, 08:37 PM   #11
A "Handy Husband"
rjniles's Avatar
Rewards Points: 904
Not sure what the value would be. More money with no benefit.
Old 04-27-2016, 08:59 PM   #12
Rewards Points: 516
If it were like a service entrance and the neutral was bonded to the EGC'S and the ground rod than there's not likely a shock hazard.
It's when EGC's are not bonded to a grounded conductor and only a ground rod when things are fundamentally wrong. *Drive a ground rod, hook up 120v to it on a 20A breaker and see what happens.
*hypothetical
Old 04-27-2016, 09:43 PM   #13
Rewards Points: 774
No benefit in having a grounded system?
Old 04-27-2016, 09:45 PM   #14
Rewards Points: 774
*hypothetical
I said treat it like a SDS. Safer based on over a 140 years experience.
Old 04-27-2016, 11:01 PM   #15
Rewards Points: 516
I'm not sure what your point is. Maybe it would help if I was more concise. A ground rod doesn't clear a fault, that's not why it's installed. Electricity takes any path available back to its source including earth. The earth has resistance. Applying voltage to earth can be dangerous. Ground rods are used to establish a connection to earth.
running ground for new upgraded 200 Amp service mbaldwin Electrical 11 05-26-2013 09:51 AM
50 Amps for a garage help IcyShadowz Electrical 48 05-31-2012 10:58 PM
Need to know if my grounds and neutrals are connected right dorlow Electrical 185 01-15-2012 02:54 PM
Ground wearing out from under garage concrete pad vernonl Building & Construction 4 05-24-2011 02:53 PM
240 volt load/appliance and ground vs neutral kgize Electrical 7 04-22-2010 11:40 PM