New Sub Panel In Garage - Electrical - DIY Chatroom Home Improvement Forum
Old 01-10-2010, 11:49 AM   #1
New Sub Panel in Garage
I am adding a new sub panel in the attached garage. The new panel is a 100A mian lug panel, I will be feeding it with a 60A 2 pole breaker from the main panel (200A service). The run from one to the other is 45ft in conduit. The question is what size conductors and ground in copper THHN. and what size conduit.
Thanks in advance for the info.
my new moneypit is offline   Reply With Quote
Old 01-10-2010, 11:57 AM   #2
I used 1" PVC - bigger then needed but bigger is easier
I went with #6 wire = 2 hots & white neutral
I used green #8 as ground but you could use #10
Old 01-10-2010, 12:01 PM   #3
If I went to 70A would #6 still be OK?
Old 01-10-2010, 12:07 PM   #4
If newer equipment/panels #6 is rated for 65a in 75c column
So as long as your calculated load is not over 65a you can install a 70a breaker
Old 01-10-2010, 12:52 PM   #5
Licensed Electrician
Magnettica's Avatar
Rewards Points: 150
Send a message via Yahoo to Magnettica
Yup. .
As long as the insulation is THWN.
Union County, NJ, Licensed Electrician
Classic Electric, LLC, Rahway, New Jersey
Magnettica is offline   Reply With Quote
Meter to Garage sub panel usajet Electrical 7 09-28-2009 10:45 PM
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
sub panel in garage - how many amps? wombosi Electrical 3 02-06-2009 10:27 PM
Wall Panel Over Sheetrock in Garage kypper Building & Construction 1 07-03-2008 07:57 AM
Breaker Panel In Detach Garage Jamn68j Electrical 2 04-25-2007 03:30 PM