Neutrals/Grounds In Main Panel - Electrical - DIY Chatroom Home Improvement Forum
Like Tree5Likes
  • 3 Post By CodeMatters
  • 2 Post By rjniles
Old 04-06-2019, 08:06 PM   #1
DIY'er
Rewards Points: 73
Question
Neutrals/Grounds in Main Panel
I am looking to install an Eaton CHSPT2ULTRA surge suppressor to my main panel (GE brand) but there is only one terminal left on the ground/neutral bar. I see almost all of the grounds are already doubled up. I understand doubling up the neutrals is a no no. The ground wire for the surge suppressor is stranded, so I take it that it should have its own terminal. Can I triple up the 14ga grounds to free up a terminal? Or can I put the stranded ground wire on the same terminal which only has one solid ground in it?
Edit: Just looked at the label on the inside of the panel and it seems to indicate that only two grounds per terminal.
gpraceman is offline   Reply With Quote
Old 04-06-2019, 09:04 PM   #2
Rewards Points: 58
I would not put the stranded wire with a solid wire. You could add an additional grounding bar attached to the panel box (be sure the bonding screw goes from the neutral bar into the box).
Wiredindallas is online now   Reply With Quote
Old 04-06-2019, 09:26 PM   #3
CodeMatters's Avatar
Rewards Points: 6,914
Re: Neutrals/Grounds in Main Panel
You could combine a few grounds in a wire nut with a single bare (equal or larger
in size to largest combined gnd) going to gnd/neutral bar.
CodeMatters is online now   Reply With Quote
Old 04-06-2019, 09:30 PM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 44
Take 4 or 5 grounds of the same size off the ground bar. Wire but them together with a pigtail of the same size, connect the pigtail back back to the ground bar.
Sent from my RCT6213W22 using Tapatalk
MTN REMODEL LLC and gpraceman like this.
My electrical answers are based on 2014 NEC, you may have local amendments.
Old 04-07-2019, 01:32 AM   #5
DIY'er
Rewards Points: 73
@Wiredindallas - Room is a bit tight in the panel to try to add another grounding bar.
I hadn't thought of doing a wire nut and pig tail as others have suggested. Seems a bit of a hack, but doing some online research, it doesn't look to be against code.
Old 04-07-2019, 11:23 AM   #6
Rewards Points: 58
It doesn't look like you have any space for a surge protector breaker. They are 2 pole thick breakers requiring a connection on both phases (240 volts). You already have all thin breakers and only 1 phase bar available.
Old 04-07-2019, 11:52 AM   #7
Rewards Points: 58
Sorry, I see you are not installing a breaker type surge protector, but you still need 2 phases for the breakers it is connected to even if hey are Hines breakers. You can move 1 existing breaker down from the other phase to get room for a 2 pole thin breaker. Is this Romex wiring or conduit? Be sure to keep any 2 hots that may be sharring the same neutral on opposite phases. If the circuit is on 2 wire Romex, no problem.
Old 04-07-2019, 01:57 PM   #8
Rewards Points: 58
Sorry. .........even if they are thin breakers..........
Old 04-07-2019, 04:33 PM   #9
DIY'er
Rewards Points: 73
There is room for more breakers in the panel. The challenge is that the ground/neutral bar is pretty full.
The surge suppressor requires a 50A double pole breaker to connect to. It looks like if I put this new breaker below that 20A double pole breaker on the bottom right that it will cover both phases. Or I could move that 15A single breaker on the left bottom down two slots and fit the new breaker there.
There is no romex. This is a direct wire from the surge suppressor to the panel. Below is a photo of the surge suppressor that I am installing. It will mount to the bottom of the panel via one of the knockouts available there.
Old 04-07-2019, 08:10 PM   #10
Rewards Points: 338
A 2-pole slim breaker will fit there. A full size double pole will fit on the bottom left.
LawnGuyLandSparky is online now   Reply With Quote
Old 04-07-2019, 11:43 PM   #11
DIY'er
Rewards Points: 73
I did manage to get the surge suppressor wired in. I pulled some 14ga grounds off of the ground/neutral bar and added a pigtail to them to free up one terminal. One terminal was so tight, I couldn't even loosen it without the head starting to strip.
The bottom photo seems to only show one LED being on. Visually, both are on. Through the camera on my phone, the two LEDs alternate being on and off. Strange.
Old 04-08-2019, 12:56 AM   #12
Rewards Points: 338
Not strange - that's alternating current.
Main Breaker Panel vs. Main Lug Panel fairmarketvalue Electrical 5 10-16-2016 08:44 PM
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 08:15 PM
Replace my main panel or main breaker? joe_oklahoma Electrical 16 12-16-2015 12:27 AM
Main Electric Panel Help Redrum Ninja Electrical 13 10-22-2011 08:28 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 12:36 PM