Need Help With Wiring Old Appliances - Electrical - DIY Chatroom Home Improvement Forum
Old 12-20-2009, 06:58 AM   #1
Rewards Points: 356
Question
Need Help with wiring old appliances
I have two older appliances that I need help with wiring. I have an an early 1980's Whirlpool stove that is currently on a 40 amp dual breaker (3 wire + GRD 120/240) and I also have a late 1980's forced air conditioning unit on a 60 amp dual breaker.
My question is what gauge wire (i.e. 8/3) should I be using for these two units? Also, I believe that stove should be on 30 amp breaker but I cannot find any specs on the unit itself. Where are the specs typically located on these units?
tripower is offline   Reply With Quote
Old 12-20-2009, 08:17 AM   #2
Remodeling Contractor
you need to determine what load and rating these units are requiring. This label is usually near the electrical access plate in the rear of the unit. you need #6 for 50 amps and #8 for 40 amps and #10 for 30 amps
Old 12-20-2009, 12:47 PM   #3
Electrical Contractor
kbsparky's Avatar
Most ranges can operate satisfactorily with a 40 Amp circuit: You can use #8/3 w/ground NM-B cable in most areas.
See if you can locate a nameplate on that AC unit. YOU are looking for 2 things:
1) Minimum circuit ampacity
2) Maximum overcurrent protection
Those will indicate your wire size and breaker size requirements.
-KB
Old 05-13-2010, 06:33 PM   #4
Rewards Points: 356
Question
Need help with oven
Here are all of the specs that I could gather on my oven:
WHIRLPOOL MODEL RB220PXK-0
30 INCH BUILT-IN CONTCNUOUS-CLEANING ELECTRIC OVEN
Kilowatts 208 volts - 3.5
Kilowatts 240 volts - 4.1
3 wire 120/208-240 volts 60hz AC only
http://shared.whirlpoolcorp.com/prod...rType=Consumer
I'm just not going to get behind that oven it is going to be a huge pain pulling it out from the cabinet. What I need to know is will the 40 amp breaker be appropriate for this oven or should I go down to a 30 amp or up to a 50 amp?
Old 05-13-2010, 07:53 PM   #5
4100w/240v = 17A, about as much as a water heater element.
The Following User Says Thank You to Yoyizit For This Useful Post:
tripower (05-13-2010)
Old 05-13-2010, 09:18 PM   #6
Rewards Points: 356
Question
Where do you get the 4100watts from?
Old 05-14-2010, 01:24 AM   #7
kbsparky's Avatar
From here:
4.1 kW = 4100 watts
-KB
Old 05-14-2010, 07:34 AM   #8
Rewards Points: 356
Question
From here:
4.1 kW = 4100 watts
Understood. So can I use a 20 amp breaker or should I use a 30 amp breaker?
Old 05-14-2010, 08:41 AM   #9
Rewards Points: 2,800
Intuitively I find it hard to believe that a "30 inch electric range with 4 burners and self cleaning oven" can run on just 20 amperes (at 240 volts). I would wire it up for 40 amps (8-3 cable).
Could it be that the name plate with the 4.1 KW rating you saw was just for the oven portion (which in my mind would result in a lot of confusion)?
The power plug may (for an older appliance) or will (for a modern appliance) indicate the maximum circuit amperes rating by its shape and size. If you strung 6 gauge wire to future proof the kitchen for a bigger 50 amp stove later, you can use a 40 amp breaker for now.
Stick to your lawn watering schedule until it really starts to pour. After the storm you have only the same number of rest days you always had and then you need to start watering again.
Old 05-14-2010, 08:47 AM   #10
A "Handy Husband"
rjniles's Avatar
Rewards Points: 710
Could it be that name plate with the 4.1 KW rating you saw was just for the oven portion (which in my mind would result in a lot of confusion)?
I believe the OP was talking about a stand alone built in oven, not a cook-top oven combo.
My electrical answers are based on 2014 NEC, you may have local amendments.
rjniles is offline   Reply With Quote
Old 05-14-2010, 09:52 AM   #11
Check it, with all switches on.
(240v^2)/4100w = 57600/4100 = 14 ohms.
Depending on the trip curve, a 20A breaker may be able to hold 17A indefinitely, but the NEC may have something to say about this.
Old 05-14-2010, 04:10 PM   #12
Master Electrician
Rewards Points: 5,082
Why would you possibly think that a 20 amp CB would not hold 17 amps indefinitely?
brric is offline   Reply With Quote
Old 05-14-2010, 05:50 PM   #13
I've run a 20a 120v breaker at 19a for my Christmas display for 5 hours without a problem
Since the stove isn't considered a continous load I don't see a problem
Old 05-14-2010, 08:35 PM   #14
I think it would, but there might be some trip curve somewhere that won't.
If this one were a 20A unit it would hold at 20.8A forever.
http://www.accontrols.com/Typical%20...ip%20Curve.pdf
Old 06-19-2010, 04:33 PM   #15
Rewards Points: 356
Exclamation
So you are saying I could run 6 gauge wire now, and use a 40 amp breaker now then later move to a 50 amp breaker when and if I purchase a oven/cooktop combo?
Wiring diagram for three-way switches with pilot light SaxTeacher Electrical 34 09-15-2013 07:53 AM
Cloth Wiring - Replace? JessicaGus Electrical 9 09-23-2009 06:45 PM
electric wiring in house remodel wis_remod Electrical 6 04-02-2009 02:40 PM
New Home Wiring - Seeking Expert Advice Dirtrnr Electrical 3 02-10-2009 10:33 AM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 07:52 PM