I have 3 wire direct bury feeder cable from a 200 amp meter base/sub panel to a 125 amp sub panel on a post 150' away and the 125 amp sub panel will feed a 30 amp RV outlet box.
The 3 wire feed was already there and I know it is not to 2008 code, but my question is: do I need to bond the neutral bar to the ground bar and to a ground rod at the 125 amp subpanel?
METZCOOL is offline   Reply With Quote
Old 03-26-2010, 09:58 PM   #2
Rewards Points: 506
I think the answer is no, because I assume the 200 amp meter base is the primary means of disconnecting your power. The location of the main disconnect is the only place where the neutral is bonded to ground.
Other replies will yield additional information.
How is the existing service non-compliant with the 2008 code?
jlmran is offline   Reply With Quote
Old 03-26-2010, 10:10 PM   #3
Here is what I am attempting:
Old 03-26-2010, 10:34 PM   #4
Rewards Points: 506
I believe this is wrong. You need an additional conductor going from the main panel to the subpanel. This additional conductor should serve as the 'effective fault path' referenced in the diagram, or in other terms, the bonding or grounding conductor. The neutral between main and subpanel should not serve as a fault-path conductor.
More bad logic: what is the purpose of the insulated stand-offs for the subpanel neutral busbar if the ground and neutral bars are bonded in the subpanel?
Old 03-26-2010, 11:19 PM   #5
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
prior to the 08 code, if you ran a 3 wire feeder to a detached building, you must install a grounding electrode and the grounding and grounded systems are to be bonded in the panel in the detached building
08 code removed the allowance to run a 3 conductor system and required a separate grounded and grounding conductor to be taken to the detached building. The grounded and grounding systems are then not to be bonded. a grounding electrode system is still installed.
if you are currently under the 08 code, your installation is illegal.
Old 03-27-2010, 06:26 AM   #6
Our township is still on 05 code, in that case the diagram is correct and and I need to bond the neutral,ground and case to a grounding rod the best I can tell ?
Old 03-27-2010, 08:23 AM   #7
Rewards Points: 506
That depends on whether you are pursuing minimal compliance or maximum safety.
Old 03-27-2010, 12:48 PM   #8
nap
You talking to me?
nap's Avatar
If you are on the 05 code, yes, you can run with only 3 conductors. The grounding electrode system (presumably a couple rods in your case), and the grounded conductor (neutral) must be bonded at the sub-panel.
Old 03-27-2010, 05:41 PM   #9
why not make it right/better since you can?
The older I get the better I was