Main Garage Supply - Electrical - DIY Chatroom Home Improvement Forum
Like Tree3Likes
  • 1 Post By rjniles
  • 1 Post By rjniles
  • 1 Post By joed
Old 04-24-2019, 03:00 PM   #1
Rewards Points: 6
Main Garage Supply
Good afternoon,
I have built a 24ft by 40ft shop at my property in Texas. I will be finishing up painting this week and will turn my focus to electrical. My main question (I'm sure I will have more) is from my main house panel to sub panel witch will be inside the shop is about 55ft. What size wire will I need to supply this shop. My plan is to have 100Amps to the sub.
Attached is a very simple (5th grade drawing) of my electrical setup inside shop.
Will 100 Amps Support this?
11- Outlets
2- 220 Outlets
8- Led shop lights
3- Dusk to Dawn Lights
1- Set of track Lights
5- Pendant Lights
Jackmac is offline   Reply With Quote
Old 04-24-2019, 04:25 PM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 210
Re: Main Garage Supply
Requirements depend on the amperage required for you 240 volt circuits but 100 amp is probably a safe bet. I would run #1/0 aluminum RHH/RHW in 1.5" PVC conduit to a 100 amp sub panel in the garage.
MTN REMODEL LLC likes this.
My electrical answers are based on 2014 NEC, you may have local amendments.
Old 04-24-2019, 04:30 PM   #3
Super Moderator
joed's Avatar
Rewards Points: 30,186
Receptacles do not use any power.
What sort of devices will you be plugging into these receptacles? Welder? AC? Dust collection? Compressor? Heat? How many amps for each device?
How many of these things might be used at the same time.
Most likely 100 amp will be sufficient.
Old 04-25-2019, 08:57 AM   #4
Rewards Points: 6
I will have a welder and an air compressor. Besides that it will be your basic garage tools most of the time nothing will be ran at the same time.
Old 04-25-2019, 09:11 AM   #5
A "Handy Husband"
rjniles's Avatar
Rewards Points: 210
Just to say a welder and air compressor means nothing. You need the amperage or wattage of the actual appliances to do a real load calculation.
Old 04-25-2019, 11:38 AM   #6
Rewards Points: 877
When I did my garage my mig welder has a 50 plug so I put in one matching receptacle and put similar plug on my air compressor so I can use same receptacle for both. The circuit breaker for this circuit is 30 amp with 10 gauge wire which is enough for each.
ddsrph is offline   Reply With Quote
Old 04-25-2019, 02:30 PM   #7
Super Moderator
joed's Avatar
That is a code violation. A 30 amp circuit must have a 30 amp receptacle.
A 50 amp receptacle can only be on a 50 amp circuit.
rjniles likes this.
Old 04-25-2019, 02:58 PM   #8
Rewards Points: 877
I was probably wrong calling it a 50 amp plug. The welder calls for AC input of 230v 20amps. Most likely a 30 amp plug. Will try to post photo. If I need to change wire and breaker it is only a two foot total run if not less.
Old 04-25-2019, 07:06 PM   #9
Super Moderator
joed's Avatar
No need to change the wire but the breaker should be changed a 20 amp. That is a normal 5-15p plug for a 15 amp circuit. It can be used on a 20 amp circuit.
Old 04-26-2019, 10:23 AM   #10
Rewards Points: 877
Joed
Are you possibly wrong about the plug on welder due to lack of scale in photo? It’s a massive plug similar in size to range plug. It has to be more than a 15 amp plug. I have taken another photo of plug in receptacle with scale.
Detached garage main vent hohadcr Plumbing 4 06-21-2017 05:47 PM
Replace my main panel or main breaker? joe_oklahoma Electrical 16 12-16-2015 12:27 AM
Garage main wont reset Jack Duren General DIY Discussions 5 12-06-2014 09:07 PM
PVC Water Main Supply to Copper Connection jdobbs Plumbing 11 02-07-2012 12:01 AM
Relocating House Main Supply Line Entry setzerr Plumbing 0 07-15-2011 07:44 PM