Junction Box Vs Pigtails - Electrical - DIY Chatroom Home Improvement Forum
Old 05-03-2010, 10:30 AM   #1
Handyman
Rewards Points: 520
junction box vs pigtails
My brother is selling his house and one of the conditions is that he get an inspection of the breaker panel. I looked at the panel and noticed that the A/C wires going into the box have been pigtailed. Would an inspector rather see, say a 4" junction box outside the panel with a another wire going straight through to the breaker. Also, I noticed that there are only two hots and a ground going to the box - no neutral. One is black, the other is white with black tape falling off of it. Any advice?
Thanks all
canadaclub is offline   Reply With Quote
Old 05-03-2010, 10:34 AM   #2
Licensed electrician
Rewards Points: 3,660
If by A/C you mean air conditioner there is no need for a neutral. Air conditioners are normally a straight 240 volt circuit.
Old 05-03-2010, 10:51 AM   #3
Electrician
Rewards Points: 910
In Canada I don't beleive you can make joints in the panel, i have always been told this but don't think i have ever read it before maybe i should look it up.
The white has been remarked to indicate that it is a hot to give you 240V.
darren is offline   Reply With Quote
Old 05-03-2010, 11:57 AM   #4
Handyman
Rewards Points: 520
Thanks so much guys...I'm wondering if maybe the junction box might be the safer way to go, you know, better safe than sorry lol
Old 05-03-2010, 12:09 PM   #5
So what is really the difference between a j-box with switches in it and a panel with breakers in it?
From what I understand, NEC allows pigtails in panels. As quoted by a poster in a similar thread...
"Splices in a panels are addressed in 312.8. Conductors shall not fill any portion of the wiring space to more than 40% of the cross sectional are of that space. Splices and taps shall not fill the wiring space more than 75% of that space."
http://www.diychatroom.com/f18/pigta...e-panel-18103/
I looked up 312.8 myself, and it basically says Enclosures can't be used as j-boxes UNLESS adequate space is provided.
So if the panel is already pretty full of wires, I could see an inspector turning down a pig-tail in the panel because it's making it over-crowded. But if there is plenty of space, then apparently there is nothing fundimentally wrong with pigtails in a panel.
HooKooDooKu is offline   Reply With Quote
Old 05-03-2010, 12:31 PM   #6
Electrician
Rewards Points: 910
I don't beleive the NEC has jurisdiction in Canada though.
Okay I looked it up
12-3032(1)
Enclosures for overcurrent devices, controllers, and externally operated switches shall not be used as junction boxes, troughs, or raceways for conductors feeding through to other apparatus.
Old 05-03-2010, 12:46 PM   #7
Okay I looked it up
12-3032(1)
The NEC has a similar concept. However, the A/C would not be feeding through. It is feed from that panel, not another panel.
Old 05-03-2010, 12:57 PM   #8
Electrician
Rewards Points: 910
Now that I read it again I have to agree with you jim, i will have to ask someone what code rule states you can't use a panel for junctions.
Old 05-03-2010, 05:29 PM   #9
Master Electrician
to the best of my knowledge they've changed the code on that in canada. I'm pretty sure you are allowed to make joints inside the panel now. There is a maximum though and inspectors do tend to frown upon it. Personally i always make joints in a seperate box. Makes for a neater installation and much easier to sort through at a later date.
edit: i double checked the rule. Looks like it only applies if your using the panel as a raceway...not if the conductors are terminated there. less than 75% cross sectional fill must be maintained though.
andrew79 is offline   Reply With Quote
Old 05-04-2010, 02:19 PM   #10
Handyman
Rewards Points: 520
Thanks for all the replies. I did install the junction box adjacent to the panel and labelled it 'air conditioning' . This also allowed me to terminate the wires on the other (less crowded) side for a much less cluttered look. Passed inspection, no problem.
Junction boxes for garage T8 fixtures mazeroth Electrical 13 01-25-2010 09:52 PM
No Power at Electronic Air Cleaner Junction Box edge10 HVAC 1 09-28-2009 07:26 PM
Light Fixture installed-no junction box? AdamsHouseCat Electrical 7 02-02-2009 11:03 AM
pigtails in Canada rtoni Electrical 13 07-24-2008 11:02 AM
Junction Question? fw2007 Electrical 10 03-31-2008 11:03 AM