Old 02-10-2010, 10:38 AM   #31
Just call me Andrew
Rewards Points: 1,032
Would using a flexible type conduit make more sense if there will be lots of turns?
Andrew
secutanudu is offline   Reply With Quote
Old 02-10-2010, 10:38 AM   #32
yes you can Amp-probe your panel while you have everything on. I have a tester its a fluke tester its a great one. it will amp probe, continuity, voltage dc and ac, its a great all aeround meter, for about 100 bucks, i wouldnt buy anything else.
www.kiesub.com/catalog/fluke-t5-600.jpg
Once you amp-probe your panel you will know more about how much juice you drawing.
longbeach1125 is offline   Reply With Quote
Old 02-10-2010, 10:41 AM   #33
Just call me Andrew
Longbeach: I have the same tester
Not sure if the jaw will fit around 200-amp cable, but I can just use the probes to test from the main breaker screw to the neutral bus.
Andrew
Old 02-10-2010, 10:54 AM   #34
good call scuba, most of the wire i have been using lately is rated both thhn and thwn
Old 02-10-2010, 12:00 PM   #35
Licensed Pro
You can measure voltage that way, but not amperage.
Old 02-10-2010, 01:15 PM   #36
Just call me Andrew
Oh, really? Amps can only be measured with the clamp meters? That is disappointing!
Andrew
Old 02-10-2010, 02:24 PM   #37
47_47's Avatar
Rewards Points: 320
four 6AWG THHN wires
Use (2)#6 blacks for hot (1)#6 white for neutral and a # 10 green for the ground.
47_47 is offline   Reply With Quote
Old 02-10-2010, 02:53 PM   #38
Just call me Andrew
Why is the ground allowed to be smaller? Just curious.
Andrew
Old 02-10-2010, 03:09 PM   #39
The ground is not supposed to carry current, so not required to be same size - my understanding
Old 02-10-2010, 03:26 PM   #40
Just call me Andrew
But if something goes wrong...it could carry as much as the breaker would allow, right? Ideally only for a split second until the breaker tripped, though.
Andrew
Old 02-10-2010, 03:28 PM   #41
Right...it would carry power for a fraction of a second...possibly a millisecond
Old 02-12-2010, 09:11 AM   #42
Just call me Andrew
I'm having some trouble understanding the table below. I see lots of different numbers in the #6 row, some as high as 75 amps allowed.
I have been told (I think) earlier in this thread that my limits are:
55 Amps - #6 nm-b (romex) - is this "TW" cable?
65 Amps - #6 THHN/THWN in conduit.
Yet I see THHN listed as 75 amps. I know I am missing something here....
Andrew
Old 02-12-2010, 09:30 AM   #43
NMB uses the 60c column
THWN/THHN uses the 75c column
Which column you use is also based on your equipment
Some (older ?) equipment is only rated for 60c
The 90c column I think is only used for service feed
Old 02-12-2010, 09:46 AM   #44
Just call me Andrew
Thanks for clearing that up. Is there a table in the NEC (I assume there is one somewhere) that shows voltage dropoff over long-distance runs? I can't seem to find it.
Also - I assume there are rules regarding placement of a subpanel (clearance from walls, etc). Where can I find those?
Thanks a lot.
Andrew
Old 02-12-2010, 09:52 AM   #45
Link to a voltage drop calc that I use:
http://www.csgnetwork.com/voltagedropcalc.html
Clearance around panel required :
Grounding a Subpanel Craigman Electrical 25 12-07-2009 07:25 PM
Problems with Square D Subpanel bltglt507 Electrical 16 12-04-2009 08:44 PM
Advice on installing a subpanel... perpetualjon Electrical 25 07-16-2009 04:47 PM
A few slightly different questions on subpanel wiring. Chris Dopp Electrical 8 06-26-2009 09:45 PM
installing a subpanel from 10/2 wire. d_skutnik Electrical 7 10-08-2008 05:35 PM