Installing an InWall Oven Electrical?
I am in the process of installing a Kitchen Aid in wall thermal oven, KEBK101SSS.
The Electrical requirements say:
http://www.kitchenaid.com/flash.cmd?/#/product/KEBK101SSS
Circuit Amps @240VAC 30
Frequency 60HZ
Voltage 208/240V
Use 8gauge solid copper wire
Also the wires coming off the oven to connect to are only 12awg
My dilemma is should I run 8awg to a 30 amp breaker, or 8awg to a 40.
Or would 10awg to a 30 amp breaker be sufficient?
Chuck
Chuck0o0 is offline   Reply With Quote
Old 04-25-2010, 08:39 AM   #2
Licensed electrician
Rewards Points: 3,658
A normal 30 amp circuit could be wired with #10. However, the NEC tells us to follow the installation instructions. You should install the #8 with the 30 amp breaker.
The insulation is different on the leads from the oven. This will account for the difference in size. The oven was also listed with those size leads.
Old 04-25-2010, 09:49 AM   #3
Electrician
Rewards Points: 910
Good luck finding #8 solid conductors, you would think the manufactuer knows that is not common.
darren is offline   Reply With Quote
Old 04-25-2010, 06:01 PM   #4
Licensed Electrician
Magnettica's Avatar
Rewards Points: 150
Send a message via Yahoo to Magnettica
#8's, 40 amp circuit breaker.
Union County, NJ, Licensed Electrician
Classic Electric, LLC, Rahway, New Jersey
Magnettica is offline   Reply With Quote
Old 04-25-2010, 06:57 PM   #5
Maybe I missed it but I did not see in the installation instructions where it states #8 required
Electric Specs from link indicate 30a
5250w = indicates only 30a needed per installation - page 4
http://www.kitchenaid.com/assets/pdf...ruction_EN.pdf
Old 04-25-2010, 09:14 PM   #6
Electrical Contractor
kbsparky's Avatar
What is the wattage on the nameplate of your oven? That determines the minimum circuit size.
(Look inside of the oven door, on the lower right side)
-KB
Old 04-25-2010, 09:38 PM   #7
Thanks for all the responses. Page 5 of in Installation Instructions states “use 8 gauge solid copper wire” in the warning box on the right side of the page. I will check on the wattage tomorrow when I get to the house.
#8 with the 30 amp 2 pole breaker seems the way to go.
Thank you all again!
Chuck
Old 04-25-2010, 10:02 PM   #8
Chuck
That is in regards to grounding the oven before working on it ?
Does not appear to have anything to do with connecting it
The Following User Says Thank You to Scuba_Dave For This Useful Post:
Chuck0o0 (04-26-2010)
Old 04-26-2010, 08:20 PM   #9
Scuba Dave, do you not agree #8 with the 30 amp 2 pole breaker is the best for this ovens requirements?
The Sticker on the oven reads:
[email protected] 120/208volts = 3.6
Kilowats @ 120/240volts = 4.7
3wire 120/208-240volts 60hzAC
Thanks all!
Chuck
Old 04-27-2010, 06:08 PM   #10
kbsparky's Avatar
A #10 wire would be sufficient in either case with the KW ratings you have supplied. 4.7kW on a 240 Volt supply is less than 20 Amps.
Using a #8 is overkill, IMO.
-KB
How do you tell if an oven is too loud? leeutwo Appliances 10 08-20-2013 09:36 PM
Gas oven problems gregsmy Appliances 1 12-03-2009 05:55 AM
Installing electrical boxes MikeyP Electrical 4 07-26-2009 09:32 AM
Counter top trim to fit with slide in oven bhagey Appliances 1 07-17-2009 08:32 AM
installing an electrical outlet with 3 sets of wires + ground dsparks Electrical 7 07-08-2009 06:18 PM