Installing A 60A Sub-panel In Detached Shed (distance 80ft) - Electrical - DIY Chatroom Home Improvement Forum
Old 06-04-2010, 05:14 PM   #1
Installing a 60A sub-panel in detached shed (distance 80ft)
Running #6 THHN; what size PVC to use? Is a ground rod necessary, and if so, is it still necessary to run a neutral and ground from main panel?
Please advise
Ebeameup is offline   Reply With Quote
Old 06-04-2010, 05:27 PM   #2
Master Electrician
Rewards Points: 5,078
Please advise
3/4" pvc is code compliant. Use 1" for an easier pull. Neutral, #10 equipment grounding conductor, and ground rods required by 2008 NEC.
brric is offline   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
Ebeameup (06-06-2010)
Old 06-05-2010, 12:24 AM   #3
Rewards Points: 1,016
I recently installed similar to my detached workshop. Bigger conduit makes for an easier pull - I used 1.5". Also allows for up-sizing if ever desired in the future. Put in a couple pull strings for future use while you are there.
Yes, you need four wires - 2 hots, neutral and ground. Yes, you have have ground rods at the sub panel. Ground and neutral are separated at the sub panel - they are only to be tied together at the main panel.
See Stubbies diagrams in the stickies for detailed interconnection drawing with comments.
The Following User Says Thank You to vsheetz For This Useful Post:
Old 06-06-2010, 09:00 AM   #4
Thank you for the reply!
One more quick question; is it ok to lay the ground rod in the trench with the PVC?
Old 06-06-2010, 09:15 AM   #5
Yes, in the case of hitting rock you are allowed to install in a trench - I am not sure of the depth requirement, let's look for someone else to respond about this.
I drive ground rods usually readily with a hammer drill.
Old 06-06-2010, 09:34 AM   #6
Rewards Points: 1,192
Pull strings for what? You can't use a sub panel for a j box,and you can't pull communication wires in with a feeder.
bobelectric is offline   Reply With Quote
Old 06-06-2010, 10:13 AM   #7
Rewards Points: 320
I would put in at least one more pipe of equal size in case you need to run phone, cable, etc out there in the future.
teamo is offline   Reply With Quote
Old 06-06-2010, 10:56 AM   #8
Yeah, once I had my trench dug to my pool cabana I ran 2 more conduits just in case
Phone, network, alarm...whatever
Old 06-06-2010, 03:17 PM   #9
My bad, was thinking of when I run data cables and such.
Garage Wiring issues jimmyfloyd Electrical 20 06-08-2009 02:57 PM
Detached shed/shop rewire gtmatt Electrical 7 05-24-2008 09:40 AM
running wire to a detached shed subpanel amakarevic Electrical 9 03-27-2008 05:15 PM
Subpanel installation in outbuilding fls Electrical 19 03-16-2008 02:19 PM
Splice in Neutral to Panel - OK or Not? allpraisebob Electrical 4 08-12-2006 05:54 AM