Hi there,
So I'm going to have 20 amps wire as long as 80 ft from the subpanel , via a junction box, to devices. Should I take "voltage drop" into consideration that it's best to install another subpanel instead of the junction box, although it cost me more to move the AC condenser which is now in the front of the junction box/subpanel location.
rockman413 is offline   Reply With Quote
Old 04-24-2019, 05:41 PM   #2
Rewards Points: 312
Re: If it's 80 ft long wire (20amps) a considerable problem for voltage drop?
should be fine - my house is over 80' long (panel is at one end) and no circuits have aver been affected by voltage drop...
found this:
If it's 80 ft long wire (20amps) a considerable problem for voltage drop?-capture.png
KPDMinc is offline   Reply With Quote
Old 04-24-2019, 05:51 PM   #3
Rewards Points: 202
found this:
Thanks. My house is like 40 feet from subpanel to junction box, and then from junction box to all the outlet it can vary from 10 feet to 40 feet, so the total length is between 50 feet to 80 feet.
By the way, I'm in Los Angeles, is the power coming into the house 110V or 120V?
Old 04-24-2019, 06:04 PM   #4
Rewards Points: 312
have to measure to find out the actual voltage
Old 04-24-2019, 06:15 PM   #5
CodeMatters's Avatar
Rewards Points: 7,362
Our code allows #12 to be used on a 20A breaker up to max length of
50m (164ft). While not code outside of Canada, this probably wouldn't
be a bad guide line.
Code ref Table 68.
CodeMatters is offline   Reply With Quote
Old 04-24-2019, 06:50 PM   #6
Licensed electrician
Rewards Points: 3,688
Nominal US voltage.is 120/240.
CodeMatters likes this.
Old 04-24-2019, 07:19 PM   #7
Rewards Points: 202
Code ref Table 68.
Is the outlet , which I think is a 20A circuit, normally is a Gauge 12 or Gauge 14 wire?
Old 04-24-2019, 07:37 PM   #8
20A breaker will normally feed #12 wire.
Old 04-24-2019, 07:39 PM   #9
Also be accurate to say North American nominal voltage is 120/240.
Old 04-24-2019, 08:24 PM   #10
Rewards Points: 202
So I'm having a 5volt voltage drop, I may end up at 115V, since most devices is made for 110V-120V, even I got this home run wires in my house up to 80 Feet, I'm still good because 115V is > 110V, am I correct?
So need to move the AC or do a subpanel, just do junction box.
Old 04-24-2019, 10:08 PM   #11
Rewards Points: 402
By my calculations you will actually drop only 2.5V over 80 feet. You are fine.
Sdiver2489 is offline   Reply With Quote
Old 04-24-2019, 11:48 PM   #12
Rewards Points: 202
Sorry, I mean, So NO need to move the ac or do a subpanel, just do a junction box.
Old 04-25-2019, 12:02 AM   #13
Rewards Points: 202
Why your calculation is very different from KPD's (see the 2nd or 3rd post)
Old 04-25-2019, 08:25 AM   #14
Deleted Member
Shadow99's Avatar
Rewards Points: 1,030
You're getting a few answers, but to properly advise you, we need the details.
Is this a 80' run to an AC unit? Most likely 240V
To do the voltage drop, we need the voltage and current of the AC unit.
If you are just running general purpose receptacles, then what @CodeMatters said will be fine.
Shadow99 is offline   Reply With Quote
Old 04-25-2019, 09:49 AM   #15
Rewards Points: 2,500
Southwire has a calculator that when I ran it for 80 feet delivering 20 amps said you need 10 awg.
Site:
https://www.southwire.com/calculator-vdrop
bob22 is online now   Reply With Quote
Digitial Timer in 3 Gang box with (2) 3way switches and 1 single pole..confused. BCS Electrical 33 03-21-2016 12:30 AM
ceiling fan wicked97 Electrical 4 08-21-2011 09:12 AM
HALP! Master/Remote Dimmer troubles! Confuserated Electrical 9 02-12-2010 04:30 PM
Pot lights in a drop ceiling Howdy Electrical 3 03-14-2008 09:23 PM
Ground Wire Problem ScubaRaven Electrical 11 06-08-2006 03:32 PM