How Should Conduit Terminate At Or Above Drywalled Ceiling? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-05-2020, 06:08 PM   #1
Rewards Points: 92
How should conduit terminate at or above drywalled ceiling?
How should conduit (PVC in this particular case) terminate at or above a drywalled ceiling? Specific case is a surface-mounted subpanel in an attached garage. Would it just be a hole in the ceiling drywall, through which the conduit passes and then simply ends with the wire coming out?
community is offline   Reply With Quote
Old 05-05-2020, 06:57 PM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 984
Re: How should conduit terminate at or above drywalled ceiling?
Are you speaking of conduit to route the branch circuits or to bring in the service conductors? If the branch conductors and the conduit is more than 24" long you might want to reconsider. Bundling branch circuits can cause you to derate the conductors below their normal amperacity.
Sent from my RCT6A03W13E using Tapatalk
My electrical answers are based on 2017 NEC, you may have local amendments.
Old 05-05-2020, 08:21 PM   #3
Licensed electrician
Rewards Points: 4,248
NEC 312.5 has conditions of conduit sleeve into surface panels. The sleeve cannot penetrate the structural ceiling.
Tags
conduit , nec code , pvc , subpanel