DIY Chatroom Home Improvement Forum (https://www.diychatroom.com/)
-   Electrical (https://www.diychatroom.com/f18/)
-   -   how long to trip? type NC 20A (https://www.diychatroom.com/f18/how-long-trip-type-nc-20a-74793/)
drgkjd 06-27-2010 06:11 PM
does anyone know how quickly (or slowly) a 20 amp FPE type NC breaker will trip when loaded to 22 AMP heating load??
i guess the right answer will be to find the "trip curve" (or characteristics) of this breaker but i could not find anything on the web
i had a kitchen circuit loaded at 22 amp (resistive) (of course, unintentionally) for about 10 minutes, the breaker did not trip. is this normal?
add: i used an amp meter to measure the current draw for each of the 2 appliances that were plugged in in steady-state; the actual total was 22.1
(for those who dislike FPE , telling me to change the panel at this point will not help-- that may come later)
Speedy Petey 06-27-2010 06:25 PM
A 20A breaker may never trip at 22A.
darren 06-27-2010 06:38 PM
It's a Federal Pacific breaker so you probably could load it up to 222A and it wouldn't trip.:laughing:
Jim Port 06-27-2010 09:25 PM
Using the trip curve for a Square D breaker loaded at 100% to 125%, the time to trip was up to several hours.
drgkjd 06-27-2010 11:31 PM
thanks....this should not be much different than i would guess. so it seems that 10% over-current can be handled easily for 10 mins and would not cause the breaker to trip in that short a time.
Originally Posted by Jim Port (Post 462171)
Using the trip curve for a Square D breaker loaded at 22 amps the time to trip was several hours. It might have even been more than that IIRC.
drgkjd 06-27-2010 11:40 PM
hmmmm...interesting....now i got to dig up a comparable trip curve and understand what is the usual overload for quick trip--- other than of course a complete short.
thanks
Scuba_Dave 06-27-2010 11:44 PM
I loaded up a bunch of C-9 Christmas light strings on a 20a circuit
I think I had 15-16 straings on the circuit
Usually they take 175w each....so at least 1625w on the circuit
I went inside...sat down & started calc'ing the load on the circuit
Realized I had too much....looked out & they were off, breaker had kicked off...maybe 15 minutes Max
frenchelectrican 06-27-2010 11:53 PM
The trip setting will affect by tempture as well like what Pete say 20 amp breaker may not trip at 22 A which I have ran into from time to time and ditto with European verison the same olé story.
but if the breaker box is in basement which I know typically more cooler than on first floor or on very warm spot it may not trip very fast with mild overload at all.
Merci,
Marc
Jim Port 06-28-2010 04:15 AM
Here is a trip curve for the 15 amp.
http://static.schneider-electric.us/...kers/730-2.pdf
As you can see it can hold 100-125% load for a long time.
drgkjd 06-28-2010 11:16 PM
thanks for posting the curve. i am pretty sure the fpe is very similar and at 10% overload it my not trip for several 1000s of second and unlikely in 10 min.
drgkjd 06-28-2010 11:18 PM
yes, the panel is in the basement....and as i see on the trip curve posted by jim, 10 min is too short for a 10% overload, specially in the cool basement (about 68deg there).