DIY Chatroom Home Improvement Forum (https://www.diychatroom.com/)
-   Electrical (https://www.diychatroom.com/f18/)
-   -   hot tub (https://www.diychatroom.com/f18/hot-tub-69132/)
dodge1972 04-15-2010 06:56 PM
hot tub
need to know how hard is it to wire a hot tub.I have a spa 50amp breker and know that I need #6 wire.
Speedy Petey 04-15-2010 07:07 PM
For me it's usually pretty easy. :thumbsup:
Maybe you can try to ask this question again with a bit of detail.
Scuba_Dave 04-15-2010 07:45 PM
There are very specific rules for installing a hot tub
Section 680 in NEC code book I think
Do you have a specific question ?
Depending upon the installation you may need a bonding grid around the hot tub
Tub must be GFCI protected
Ground must be insulated
#6 wire must be correct color, can't be remarked
dodge1972 04-15-2010 09:07 PM
hot tub
Have a 50 amp breaker with gfci and a 50 amp double pole breaker for panel.was wondering if it is hard to wire the tub or is there anything else I need besides the #6 wire to do the job.thanks
Speedy Petey 04-15-2010 09:54 PM
Originally Posted by dodge1972 (Post 429234)
.... or is there anything else I need besides the #6 wire to do the job.
Yes, there is a lot more needed.
frenchelectrican 04-15-2010 10:46 PM
I done few of hot tub hook up however let me address couple things along the way.
• mantory RCD { GFCI }
• No bare grounding conductor in the conduit in outdoor locations at all.
now next step is the location of subpanel or disconnect switch most useally are 5 feet away but no more than 10 feet away but let me warn ya check with your local codes it may spell diffrent than what myself and other posted the info here.
Is this spa will be on the ground or on the deck { this part if on the deck you will have to check the stucture to see if they can hold addtional weight typically most spa I know they hold about 750 liter { apx 200 gallons } and can weight up more than 2,000 lbs { water weight in 8.0 lbs per gallon }
Also if you have any overhead conductors or cable there is spefic rules dealt with that.
just ask us more question we will be more than happy to answer the question.
More the details you provide us the better the answer we can able give to you.
Merci,Marc
{ above items are in North America side the French codes is little more tighter than this }
mpoulton 04-15-2010 10:56 PM
So you have a 50A breaker for the main panel, 6/3 wire (red/blk/wht/bare) for the run from the panel to the hot tub, and you have a 50A GFCI breaker for the tub disconnect/GFCI protection. Is that GFCI breaker a complete hot tub "kit" in its own disconnect enclosure, or is it just a bare breaker? Obviously you need the enclosure for it. Aside from general hardware like wire staples and strain reliefs, that should do it.
It sounds like you already sort of know how to do this, since you bought the right parts. The 50A breaker goes in your main panel. The 6/3 wire must be routed according to code (strain relief at the panel and disconnect, secured properly, protected from damage, etc.). Mount your GFCI disconnect enclosure near the tub (see NEC rules on location) and run the wire into the back of it. If the hot tub has a "whip" for power already, run it to the disconnect enclosure using appropriate hardware (lock nut or strain relief, as required). If it does not have a whip, you will need to make one - use 3/4" or 1" nonmetallic flex and individual stranded #6 THHN/THWN conductors.
The red and black wires in the 6/3 from the main panel connect to the "line" side of the GFCI breaker. The white wire connects to the neutral bar in the disconnect enclosure. The neutral bar must be separate and isolated from the ground bar. The hot tub's red and black connect to the "load" side of the GFCI breaker. The GFCI breaker's neutral wire must go to the neutral bar, and the hot tub's neutral (if it has one) must connect to the GFCI breaker's neutral terminal. If it does not require a neutral, ignore it. All of the grounds connect to the ground bar in the enclosure. That's it.
J. V. 04-16-2010 01:07 PM
1 Attachment(s)
If I were doing this job, I would use the 50 amp two pole breaker to feed this.
Knucklez 04-18-2010 10:19 PM
4 Attachment(s)
NEC Section 680.26 for required Bonding grid around the pool/spa
can anyone discuss this in more detail?