Grounding Conductor For Service Must Be # 4 Copper Wire - Electrical - DIY Chatroom Home Improvement Forum
Like Tree1Likes
  • 1 Post By brric
Old 04-21-2019, 08:27 PM   #1
Rewards Points: 534
Grounding conductor for service must be # 4 copper wire
This the note that the inspector left when came to inspect the electrical installation on a double wide mobile home.
Can someone please correct me if I am wrong, but I thought # 4 should be for aluminum wire and for copper wire should be # 6 - according to the code book correct?
This is for residential installations.
form8829 is offline   Reply With Quote
Old 04-21-2019, 09:39 PM   #2
Master Electrician
Rewards Points: 4,910
Re: Grounding conductor for service must be # 4 copper wire
Service size and type of grounding determines conductor sizing. NEC never requires larger than #6 copper to grounding rods. Local requirements may differ. Never use aluminum conductors for grounding if they are at or below grade.
brric is offline   Reply With Quote
Old 04-22-2019, 09:43 AM   #3
Rewards Points: 534
I guess my other question will be, is the inspector referring to the main conductors from the outside panel to the inside?
Old 04-22-2019, 08:36 PM   #4
Rewards Points: 2,730
What was the inspector saying (words verbatim, not asking you to read his mind) when you thought he might be referring to the main conductors from the outside panel to the inside?
Incidentally if there is a panel or box with a whole house shutoff outside under the meter then there must be 4 conductors -- two hots, neutral, and ground -- running from there to any inside panel which may be large and may be the primary panel for the house branch circuits.
Heat went off in the dead of winter? Excellent idea to be late or absent for work and to spend the day winterizing your house to keep pipes from freezing. Every house is different. For those of you not hit yet, think of what things you need to do.
Old 04-23-2019, 01:04 AM   #5
Licensed electrician
Rewards Points: 3,592
What size is the service you are installing? Is the grounding for a metallic water.line or to a rod?
Old 04-23-2019, 05:49 PM   #6
Rewards Points: 534
he actually was referring to the conductor that goes to the grounding rods.
Old 04-23-2019, 08:33 PM   #7
Rewards Points: 58
The ground from the 1st means of disconnect past your meter needs to be #4 copper if it is a 200 amp service (2/0 or 3/0 hot conductors).
Wiredindallas is offline   Reply With Quote
Old 04-23-2019, 09:07 PM   #8
Master Electrician
Not to grounding rods per NEC.
jhil likes this.
Old 04-25-2019, 02:36 PM   #9
Rewards Points: 362
Per the NEC it depends on the size of the service-entrance conductor. Safer to go with 4 AWG wire as the cost difference is trivial at less than 40 cents a foot in savings.
Where I use 6-gauge is when I need to bridge a valve or water filter put in a jumper wire to maintain the ground continuity of copper pipe.
Calson is offline   Reply With Quote
Old 04-25-2019, 05:21 PM   #10
Master Electrician
Another incorrect statement. The NEC does not require larger than #6 copper to grounding rods, regardless of the service size. Upsizing provides no additional protection.
Old 04-25-2019, 09:59 PM   #11
The #6 to bond over a meter is not large enough on a water line ground.
The NEC never requires anything larger than #6 to a ground rod. You are not getting any additional safety by using #4.
Digitial Timer in 3 Gang box with (2) 3way switches and 1 single pole..confused. BCS Electrical 33 03-20-2016 11:30 PM
House grounding wire near/touching gas pipe. Safe? CardCoder502 Electrical 20 01-10-2014 05:03 PM
yet another 3 wire range hookup question - grounding receptacle plate/box? rkg Electrical 7 04-03-2012 01:02 AM
Need to know if my grounds and neutrals are connected right dorlow Electrical 185 01-15-2012 02:54 PM