Old 01-18-2010, 03:41 PM   #1
Bigplanz's Avatar
Rewards Points: 2,492
GFCI confusion
I have a GFCI circuit in the basement. One of the downstream receptacles had a cracked plastic face plate, so I decided to replace it with a metal one. When I took the cracked face plate off, one of my fingers brushed a hot brass screw and I got shocked. Yet, the leak to ground did not trip the GFCI. I pushed the GFCI test button and it tripped. I tested the receptacle that shocked me with a GFCI receptacle tester and it glowed double green. When I pushed the test button, it tripped, just like it's supposed to. Yet, it didn't trip when I grounded it by brushing against the hot screw. WTF?!?!?
Bigplanz is online now   Reply With Quote
Old 01-18-2010, 03:59 PM   #2
the Musigician
DangerMouse's Avatar
you got shocked BEFORE it was protecting?
DM
Old 01-18-2010, 04:06 PM   #3
Make sure it is off the LOAD side of the GFCI & not the LINE side
Old 01-18-2010, 04:38 PM   #4
Tool Geek
PaliBob's Avatar
Rewards Points: 2,160
Big tested the outlet in question with a GFCI Tester and it tripped the upstream GFCI so there is no Line/Load mix-up.
The shock was most likely from a very low level current that could take up to several seconds to trip the GFCI.
http://ecmweb.com/mag/electric_think_gfci/
Disclaimer
& Stay Safe
.....Bob Lavery
Old 01-18-2010, 04:46 PM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 2,006
A GFI is NOT intended to prevent shocks. It is intended to prevent electrocution.
Old 01-18-2010, 05:04 PM   #6
Inspector/Instructor
codeone's Avatar
Agree totally!
codeone is offline   Reply With Quote
Old 01-18-2010, 05:28 PM   #7
Bigplanz's Avatar
Yes, I know, thank you. However, it should trip at a threshold so low that if one felt a shock it would be almost imperceptible. This felt like any other 120V shock I have ever gotten. Made me jerk my hand away and go "Ow!"
Old 01-18-2010, 05:36 PM   #8
Too Short? Cut it Again!
You sure the two are on the same circuit?
Old 01-18-2010, 05:45 PM   #9
Just call me Andrew
Rewards Points: 1,032
He knows that outlet is protected since it tripped with the tester.
Andrew
secutanudu is offline   Reply With Quote
Old 01-18-2010, 06:05 PM   #10
Absolutely not. A shock is a shock. It depends on how well you are "grounded" and how much current feeds through you. You "feel" the voltage, not the current.
If you are not grounded very well then you will not get much voltage. Similar to voltage drop.
Current flow trips the GFI. The GFI trips if it measures 5-6mA of current imbalance between the hot and neutral (or hot and hot). This 5-6mA can be leaking many places, including through your finger. It will trip in a very short time period, so it is completely feasible that you will get a very painful shock but not for nearly enough time to kill you.
Old 01-18-2010, 06:53 PM   #11
I'll be the devils advocate here
1. You were working hot. The safest practice would have been to shut the breaker off prior to work. Thus no chance of a shock.
2. GFCI and other safety devices must be designed to prevent injury/death BUT avoid nuisance tripping. Many old (and even new) pieces of electrical equipment (usually things with large motors) will trip a GFCI. If GFCIs were designed to a more stringent set of parameters there would be even MORE nuisance trips.
DownRiverGuy is offline   Reply With Quote
Old 01-18-2010, 06:53 PM   #12
Bigplanz's Avatar
It appears from this article that one 'feels' the current, rather than the voltage. However, Table 2 of this article indicates that one registers a shock at 1.8 mA so I guess I got zapped at below a 5 mA level.
http://www.highvoltageconnection.com...kQuestions.htm
Old 01-18-2010, 07:19 PM   #13
Tool Geek
PaliBob's Avatar
BIG p, Thanks for posting the 'Shock' link.
I Bookmarked it
Disclaimer
& Stay Safe
.....Bob Lavery
Old 01-18-2010, 07:54 PM   #14
I guess you could say it is a combination of the two. It HAS to be. One is nothing without the other.
I just always laugh when someone throws out that old line "It's the amps that get you".
Old 01-18-2010, 08:08 PM   #15
Question
As a matter of fact it states so in the insert that comes along with the GFCI receptacle, That "You might feel a shock even if the receptacle will trip"!!
spark plug is offline   Reply With Quote