Generator Transfer Switch Sizing - Electrical - DIY Chatroom Home Improvement Forum
Old 01-27-2015, 02:27 PM   #1
Rewards Points: 320
Generator transfer switch sizing
Hi All,
I bought a Champion model #41537 generator. It is listed as 7500 running watts/9375 starting watts. I am going to install a manual transfer switch/panel and a power inlet box on the house in a few months when it warms up outside.
I am doing my research now looking at some of the usual types: Generac, Reliance, etc.
The generator is listed as roughly 30 amps (7500 watts/240 volts=31.25 amps).
1. Should I size the transfer switch/panel at 30 amps or use the starting wattage 9375 watts/240 volts= 39.62 amps, and up size the panel to a 50 amp model?
Not sure where I am going to put the power inlet box. I could put it on the house and have about a 25' run across the cellar to the panel or I could mount it on the exterior of the detached garage and use a 1" pvc spare conduit that I laid in the ground years ago. The garage option would be approx. 100' to the panel. I calculated the voltage drop @ 30 amps to be about 2.69% with #10 copper wire.
2.Should I up size to #8 copper or is this an acceptable voltage drop?
teamo is offline   Reply With Quote
Old 01-27-2015, 03:08 PM   #2
Oso954's Avatar
Rewards Points: 1,250
You will be fine with 30 amp equipment.
I would choose the shorter routing from inlet to panel. Remember that you also have a generator cord X feet long from the inlet to the Generator.
Your generator has a 30 amp breaker for the 240V receptacle. It will trip if you exceed the 30 amps for too long.
The surge capacity is primarily intended for a brief overload caused by motor(s) starting.
Oso954 is offline   Reply With Quote
Old 01-27-2015, 03:10 PM   #3
Rewards Points: 768
You can always "upsize" the transfer switch and associated wiring. Then if you ever get a bigger generator you're all set. The generator is protected by it's own breakers.
If you use a 50 amp inlet and only have a 30 amp receptacle on your generator, make a transfer cord that will "adapt" the two.
Don't plan on running a portable generator at full load for an extended period or it won't last.
AandPDan is offline   Reply With Quote
Old 01-27-2015, 03:17 PM   #4
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Is that legal? lol....
Old 01-27-2015, 04:33 PM   #5
Rewards Points: 768
You don't need a generator to put in a transfer switch.
Old 01-27-2015, 04:44 PM   #6
dmxtothemax's Avatar
Rewards Points: 7,736
Yes it is ?
Other way round could be another story thou !
dmxtothemax is offline   Reply With Quote
Old 01-28-2015, 08:40 AM   #7
Rewards Points: 320
Thanks all for the help.
Old 01-28-2015, 11:38 AM   #8
Rewards Points: 3,396
Is 30 amp rated equipment rated for over 30 amps if not for too long ? Especially 10 amps over
ritelec is offline   Reply With Quote
Old 01-28-2015, 01:54 PM   #9
Oso954's Avatar
If it isn't, everyone is in trouble.
What (approximately) do you think the trip time is on a 30 amp 240V breaker with a 40 amp load ?
Old 01-28-2015, 07:59 PM   #10
Rewards Points: 1,414
If it's not much additional work, put it closest to where you will be able to leave the generator running. You don't want to be stepping over an extension cord for a week if you have power go out.
Plan for the carbon monoxide buildup and, depending on your neighborhood, on having something to lock the generator to.
Tom738 is offline   Reply With Quote
Old 01-28-2015, 08:48 PM   #11
HMMMMMMMMMM... do you know the answer ???... I'm gonna make a WILD guess at......hmmmmmmm..............5 seconds
Old 01-29-2015, 12:10 AM   #12
Oso954's Avatar
It could be that quick, or longer. There isn't a one right answer as there are variables involved.
But, if I use the 5 seconds, that makes the exceeding the rating time 5 seconds before the generator breaker opens or the OCD in the transfer panel opens.
The breakers are doing their job to remove the overload, before the safety margin is gone.
The generator surge ratings are there for two reasons, to let motors start and the marketing departments find that the bigger the number you put on the side of it, the better it sells. Most purchasers do not realize how short of a time that surge power is really available.
In practice, the OP is going to find that he will have to keep loads below 30 amps or a breaker will trip. And when running big loads (or a combination of loads), you sometimes have to kill the breakers on refrigerators, A/C or other thermostat controlled loads to keep them from auto-starting while the other big loads are running. Otherwise you are making a lot of trips to reset breakers.
Old 01-29-2015, 04:38 PM   #13
Rewards Points: 320
"If you use a 50 amp inlet and only have a 30 amp receptacle on your generator, make a transfer cord that will "adapt" the two".
I was thinking of using a 50 amp set up in case I go bigger in the future. Instead of making the adapter cord now I can use a 30 amp inlet and run #6 copper to the transfer switch. Either way it will cost about the same to buy the receptacle end or buy a new power inlet box if and when that time comes. If I decide to get a bigger generator in the future then I will only have to change out the power inlet and the wire will be all set. Another question: Do I need to use service type cable from the power inlet to the transfer panel or can I use 6-3 nm copper? I can also pipe it with pvc or emt with #6 thhn/thwn.
I know that I am going to have to manage the loads closely while on generator power. Luckily the history of power loss in my area has been of relatively short duration, usually 3-5 hours with the longest I remember being about 12 hours in the last 12 years that I have lived here. Of course there is always that future storm that could change all of that which is what I am preparing for.
Wiring in a 4-way Switch RickSene Electrical 6 05-13-2017 04:29 PM
A few wiring questions on installing this timer switch thinksincode Electrical 19 03-04-2013 05:31 AM
Carrier Infinity 69 Trouble Code 42 bodya1 HVAC 4 12-05-2010 06:43 PM
3-way light with a twist Jeepsail Electrical 14 05-18-2010 01:24 AM
4 way switch confusion Richo Electrical 10 04-09-2009 07:11 AM