Garage Breaker Box Problem - Electrical - DIY Chatroom Home Improvement Forum
Like Tree3Likes
  • 3 Post By Kkeyz
Old 10-06-2017, 10:04 AM   #1
Hi all, I'm posting from NJ. Abour a month ago I started having odd problems in my detached garage. I have problems on multiple circuits that involve low voltage. LED lighting started flickering, fluorescent lighting would flicker but not light. A refrigerator's lights would light dimly, and the compressor/fan would not run. It happened earlier this year for a day, then it resolved on its own. Now the problems are back.
I've ruled out wiring problems and was testing voltage between the ground, hot and common lines in the box, and as soon as I made contact with the tester between (I think) the hot and common lines in the breaker box, all the lights came on, and the fridge started working. Unfortunately I had to leave for work, so I shut off the garage breakers, and left. This morning the problems are all back. Does anyone have an idea of what I'm dealing with? Thanks in advance for any help...
Kkeyz is offline   Reply With Quote
Old 10-06-2017, 10:30 AM   #2
Super Moderator
joed's Avatar
Rewards Points: 30,972
Re: Garage Breaker Box Problem
Bad neutral connection. Either a connection at the garage or house end, or bad underground cable.
If you measure any voltage ground to neutral then that pretty much confirms it. Ground to neutral should be zero volts.
Old 10-06-2017, 10:40 AM   #3
Mike Milam's Avatar
Rewards Points: 146
My younger brother (R.I.P.) buried alum. wire from his house to his detached garage once. I warned him not to in advance, but what did I know? The ground was bare alum. Called me one day and said lights were dim and when he turned the bench grinder on everything came back on. I went over there and opened his breaker box, leaned my hand on the furnace near by and it knocked the crap out of me. He had to dig the lines up and replace them.
Thank a police officer for being the one who runs 'TO' a report of shots fired, while everyone else runs 'AWAY'
Mike Milam is offline   Reply With Quote
Old 10-06-2017, 11:48 AM   #4
CodeMatters's Avatar
Rewards Points: 7,696
Stick to the simple stuff. Expect your garage has a 3 wire +gnd feed. Check
the tightness of these 4 terminations at both ends. Likely to be either a loose
hot(leg) or neutral.
BTW, it was likely the mechanical pressure you applied with your
tester that made things work so I'd suggest starting in that area.
DVM are very high impedance (when set for volts) so it's unlikely
the DVM had an electrical effect on the cct.
CodeMatters is online now   Reply With Quote
Old 10-06-2017, 08:34 PM   #5
Thanks everyone for your quick responses. It was a loose neutral connection coming in to the garage.
Mike Milam, Nealtw and CodeMatters like this.
Service to Garage options - feedthrough panel, dual lug meter, subpanel crazyjpeters Electrical 4 04-13-2015 06:50 PM
3 way switch trips breaker over night Hazelberg Electrical 5 09-21-2012 09:34 PM
Garage Fridge Tripping Breaker in Cold Weather aaronjwood Electrical 10 12-24-2010 06:47 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
Problem with circuit breaker. HELP! spartanic Electrical 2 10-28-2007 03:09 PM