Old 09-20-2014, 10:04 PM   #16
Rewards Points: 1,832
Originally Posted by Speedy Petey View Post
When you sell a H-I will probably call it out and someone will come along ans say it's fine.
I still get veteran electricians saying it's fine, which amazes me.
Same. Back then a lot of people just didn't understand it well, even SEU was misused originating from subpanels.
Jump-start is offline   Reply With Quote
Old 09-21-2014, 03:58 AM   #17
dmxtothemax's Avatar
Rewards Points: 7,822
So is the wire an earth or a neutral ?
If it is a 240 circuit
it doesn't need a neutral .
dmxtothemax is offline   Reply With Quote
Old 09-21-2014, 05:02 AM   #18
A "Handy Husband"
rjniles's Avatar
Rewards Points: 804
As he describes it, it is a bare ground being used as a neutral. Dryers (in the US) are 120/240.
I would replace the NM section with 10/3 and pull a #10 ground and neutral (2 wires) into the pipe using the the bare ground as a pull wire. And install a 4 wire receptacle.
My electrical answers are based on 2017 NEC, you may have local amendments.
The Following User Says Thank You to rjniles For This Useful Post:
csab_ (09-21-2014)
Old 09-21-2014, 09:49 AM   #19
The bare wire is an earth if it is found in NM-B. If it is SEU, and it comes from the main service disconnect, its ok. Why bare SEU is allowed to carry current and not NM-B? I don't know, but id say its more of a listing thing being more a technical violation in the NEC. I know of entire multi hundred condo divisions and cookie cutter homes built with the incorrect wire (10/2w/g 6-2wg) for dryers and ranges still going without issue. However, it was never code allowed.
Nearly all US designed dryers need both 120 and 240 unlike Euro models that only need 230 volts. In the US up until the 1996 NEC it was allowed to use the insulated neutral conductor or the neutral in SEU to ground the metal frame.
One reason why SEU might be allowed to carry current and not NM-B that before ranges and dryers SEU all the way up to the present day was/is allowed in millions of services where the concentric neutral carries current. Im guessing he thought was back then: if it can carry current at the service why not a range or dryer? NM-B became popular latter, and at first came with an undersized ground.
Old 09-21-2014, 01:14 PM   #20
Rewards Points: 637
I'm not putting any money and work into this while we don't need the receptacle. I keep it legal with the blank plate. I'll think about it again when we are selling the house or if my wife wants a dryer.
But thanks for the repair suggestion! I'll remember it for the future.
csab_ is offline   Reply With Quote
Old 09-21-2014, 05:17 PM   #21
Originally Posted by petey_c View Post
Plenty of older dryers/ovens/ranges were wired correctly and legally with SEU type cable, not NM.
I would guess that if it's a 240 only load
then it doesn't use the earth as a neutral
It would be ok under those circumstances
But it seems that now days they do use 120 & 240
so a neutral is required.
Under these circumstances it would be a problem.
Old 09-21-2014, 06:22 PM   #22
Rewards Points: 382
dmx, nearly all electric dryers that have ever been sold in the U.S. use 240V only for the heat. Everything else -- the motor, the timing circuits, and accessories like drum lights -- operates on 120V. So they all need a neutral.
fa_f3_20 is offline   Reply With Quote
The Following User Says Thank You to fa_f3_20 For This Useful Post:
Speedy Petey (09-22-2014)
Old 09-21-2014, 07:45 PM   #23
Licensed electrician
Rewards Points: 3,766
The bare concentric conductor from SE cable is a neutral, not the ground although it can be also used a a grounding conductor on a straight 240 volt load. The bare in NM is only a ground.
Old 09-21-2014, 09:37 PM   #24
Very true, also just to add for those reading SEU can not originate from a subpanel when feeding an old 120/240 volt dryer or range.
Old 09-22-2014, 06:15 AM   #25
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
To understand some of the NEC codes, you have to travel back in time when they were adopted, this one is an easy one….. It was because of the war, raw materials were being used during this time period, so to save on material, they allowed SEU to be re-bonded at the appliance and eliminate the extra conductor….
When we got to 1996, the code panels decided the war was over, and eliminated this special rule from the NEC.
Now…. why people violated that rule by using NM was a misunderstanding of what was actually allowed, just like any code in the NEC, if you learn the code from your co-worker or boss, there is a good chance you are going to be misinformed.
The Following User Says Thank You to stickboy1375 For This Useful Post:
clw1963 (09-22-2014)
Old 09-22-2014, 06:19 AM   #26
E2 Electrician
And this has logic behind it as well, In the US, we have multiple voltages within the US, If they made strictly 240V dryers in the US, they would not work very well with a 208v service, the heaters would work fine but at a reduced output, but the motors, not so well…. It is much cheaper for a manufacture to purchase a 240v motor vs a 240/208v motor, and profits decides everything!
It is much cheaper for a manufacture to produce one unit than two different models at different voltages….
Box Size for Dryer Receptacle sirsparksalot Electrical 12 05-02-2011 09:36 AM
Re-route dryer electric cable Stu27 Electrical 10 09-06-2010 08:21 PM
4-prong dryer receptacle algraz Electrical 2 08-10-2009 03:04 PM
Bringing 220 volt dryer receptacle upstairs... danthemandan Electrical 5 02-03-2009 11:52 AM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 11:33 AM