I need a DP thermostat that thermostatically breaks BOTH lines. i.e. the Honeywell T410B or Dimplex TD 322W only break one line thermostatically and the other is only broken in the OFF position.
I am using the thermostat to control a 24 VAC zone control valve and simultaneously turn on a 115 V fan switch. in a hydronic heating system.
docdoor is offline   Reply With Quote
Old 10-21-2010, 12:45 PM   #2
Rewards Points: 2,800
You should get a contactor (relay) that uses one input and can switch two other circuits on or off as needed. The input (feeds a coil) must accept the voltage and amperage (current) that the existing thermostat provides.
They make direct switching (line voltage) thermostats used with electric baseboard heat. Usually each has two built in switches. You could use one half of the thermostat for the 24 volt circuit and the other half for the 115 volt circuit.
But the two switches usually don't click on and off at precisely the same time or temperature.
Stick to your lawn watering schedule until it really starts to pour. After the storm you have only the same number of rest days you always had and then you need to start watering again.
The Following User Says Thank You to AllanJ For This Useful Post:
docdoor (10-21-2010)
Old 10-21-2010, 01:06 PM   #3
Licensed electrician
Rewards Points: 3,662
I must be missing something here, but, this sounds like for baseboard heaters.
A SP t-stat only breaks one side. A double pole t-stat breaks both sides. Both should be readily available.
Old 10-21-2010, 02:02 PM   #4
DP Thermostat
The thermostats that are advertised as DP i.e. Honeywell CT410B or Dimplex TD322W are not truly DP in the sense that the poles don't switch simultaneously as with a relay, they are more or less two switches one that is thermostatically controlled (only one of the lines, black wires), and the other (line, red wires) that is not, in that it only cuts the power to the device (of the one line, red wires) in the OFF position. in other words when the thermostat is not calling for heat one line will be disconnected (black wires) but the other line will not (red wires), thus allowing voltage to the device along the one line (red wires). I don't need simultaneous activation, a slight delay would be acceptable. Now in my application I am attempting to control two separate devices thermostatically, one is 115VAC (fan) and the other 24VAC (solenoid valve).
Old 10-21-2010, 02:54 PM   #5
A "Handy Husband"
rjniles's Avatar
Rewards Points: 704
Use the T-stat to control a DPST contactor (relay) with a 24 volt coil and contacts rated for 120 volts. Use one contact for the zone valve(24 VAC) and the other for the fan(120 VAC).
My electrical answers are based on 2014 NEC, you may have local amendments.
The Following User Says Thank You to rjniles For This Useful Post:
Carrier Edge Thermostat Installation Issue ptalar HVAC 1 07-13-2010 05:40 PM
Honeywell Prestige HD thermostat wiring 1H/1C + Humidification System TekGamer HVAC 0 07-09-2010 11:58 PM
Problem with Lennox Pulse Furnace Wiring to Thermostat scalvin Electrical 4 12-30-2009 07:48 PM
Replacing thermostat...................... sktn77a HVAC 6 09-02-2009 10:07 PM
Thermostat from Manual to Digital trinamillersmit HVAC 5 07-02-2009 09:21 AM