Does Temperature Influence The Effectiveness Of A Circuit Breaker? - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-10-2015, 03:28 PM   #16
Rewards Points: 1,832
Originally Posted by InPhase277 View Post
Look who posted it. Are you surprised?
No. But Id rather the OP get a correct answer. It doesn't matter anyways since we are all on block. In two weeks we'll see this same answer in a new thread.
Jump-start is offline   Reply With Quote
The Following 3 Users Say Thank You to Jump-start For This Useful Post:
InPhase277 (10-10-2015), Jim Port (10-11-2015), NotaDIY/Pro (10-10-2015)
Old 10-10-2015, 04:01 PM   #17
Rewards Points: 201
Originally Posted by Jump-start View Post
Not true, there is also a thermal component:
http://goodsonengineering.com/wp-con...rMyths_web.pdf
The magnetic component usually starts around 10x the breaker's handle rating and that is intended for short circuits. Overloads like a 30 amp load on a 15 amp breaker are via bi-metallic strip.
All accurate, and it goes even further. For a long time there were breakers sold that didn't have a magnetic trip system at all. One way to know that Jump-start is right, without having to know breaker engineering, is to notice that overloads don't trip breakers immediately. Short circuits do, but overloaded circuits can take minutes to trip. Why? Because the breaker has to warm up enough for the bimetal strip to move.
Run and find ou is offline   Reply With Quote
The Following User Says Thank You to Run and find ou For This Useful Post:
Jump-start (10-10-2015)
Old 10-10-2015, 04:15 PM   #18
Rewards Points: 201
Originally Posted by NotaDIY/Pro View Post
Where is this "rule" you speak of? I would be interested in your research regarding such. Please post.
National Electrical Code, 210.20(A), at least that's the section number in the 2011 edition.
micromind (10-10-2015)
Old 10-10-2015, 04:33 PM   #19
Rewards Points: 50
Has nothing to do with some "80% rule". Thanks for trying.
NotaDIY/Pro is offline   Reply With Quote
Old 10-10-2015, 04:59 PM   #20
The NEC defines what is a continuous and none continuous load. Where the load is continuous the circuit can only be loaded to 80% of the handle rating.
What do you have in mind?
The Following 2 Users Say Thank You to Jump-start For This Useful Post:
Jim Port (10-10-2015), micromind (10-10-2015)
Old 10-10-2015, 05:16 PM   #21
Rewards Points: 2,005
Correct , the general rule is 80% for continuous load . I always figured the requirement for an external Main had more to do with the wishes of the fire department than the electrical utility .
God bless
Wyr
WyrTwister is offline   Reply With Quote
The Following User Says Thank You to WyrTwister For This Useful Post:
Old 10-10-2015, 05:52 PM   #22
Rewards Points: 201
It says not less than the non-continuous load plus 125% of the continuous load. So, a continuous 16 amp load would require a 20 amp breaker (1.25 * 16 = 20). 16 amps is 80% of the breaker's nominal capacity (0.8 * 20 = 16). If the load were completely non-continuous then a 20 amp load could be served by a 20 amp breaker. In other words, breakers are derated to 80% when serving continuous loads. Are you looking for something else?
Old 10-10-2015, 07:29 PM   #23
Idiot Emeritus
Rewards Points: 80
210.20(A) Continuous And Noncontinuous Loads. Where a branch circuit supplies continuous or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125% of the continuous load.
The inverse of 125% = 80%.
This is generally referred to as the '80% rule' because in a lot of instances a breaker cannot be loaded to more than 80% of its rating.
There are exceptions of course.........
P.S. Article 100 defines a continuous load as a load where the maximum current is expected to continue for more than 3 hours.
One notable exception is 422.13 Storage Type Water Heaters. A fixed storage-type water heater that has a capacity of 120 gallons or less shall be considered a continuous load.
The idea of breakers transferring their heat to adjacent breakers is somewhere in the UL White Papers and is the basis of the 80% rule.
micromind is offline   Reply With Quote
The Following User Says Thank You to micromind For This Useful Post:
Run and find ou (10-10-2015)
Old 10-10-2015, 08:08 PM   #24
Rewards Points: 50
Well, I will concede. However, Mike Holt says otherwise. Just never heard of using the inverse of 125% to accomplish load calcs, perhaps there is something to it, I really don't know. Could be there is something to learn here, but not seeing it.
Old 10-10-2015, 09:32 PM   #25
Licensed electrician
Rewards Points: 3,766
Originally Posted by gregzoll View Post
The only place in above the 38th parallel north that you would see outdoor disconnects is RV & Mobile Home parks, or on Farm properties around dryers, grain elevator equipment, farm animal housing.
Might have to go back and tell my customers that their house is actually a RV or in a trailer park . Boy did the realtor get one over on them. Imagine 300 and 400K dollars for a trailer.
InPhase277 (10-11-2015)
Old 10-11-2015, 04:18 AM   #26
Just mathematics . Does not matter who said what .
16 amp continuous load x 125% = 20 amp Circuit Breaker
20 amp CB x 80% = 16 amp continuous load
God bless
Wyr
micromind (10-11-2015)
Old 10-11-2015, 09:23 AM   #27
Rewards Points: 2,350
Another place you won't find outside disconnects is on ships. When Greg was in the Navy, he did electric work on boats and they never had disconnects in the middle of the ocean, therefore it can't happen anywhere else. Did you know Greg was in the Navy? If need be, he can ask an old Navy electrician on another forum to make sure. But at any rate, Navy. Navy trumps all. Just... Navy.
Old 10-11-2015, 10:29 AM   #28
Don't forget about all the rooftop HVAC units out there for the malls and office buildings and restaurants. I guess you didn't remember those .
Around me almost all the roofs are outside. You did say ONLY didn't you? Wouldn't want to be accused of trolling.
The Following 2 Users Say Thank You to Jim Port For This Useful Post:
InPhase277 (10-11-2015), Jump-start (10-11-2015)
Old 10-11-2015, 11:06 AM   #29
He does have a lot of experience with floating neutrals though.
Circuit breaker keeps immediately tripping after reset... Ler0y Jenkins Electrical 30 05-22-2013 01:17 PM
does a household circuit breaker have thermal memory? djmieczk Electrical 40 02-10-2013 06:59 PM
Circuit breaker not returning everything to power after switched back on sam112 Electrical 7 02-10-2013 12:48 AM
New wiring tripping breaker on another circuit? Kinggofg Electrical 11 04-26-2012 01:36 AM
Condensation amyevans Windows and Doors 6 10-21-2011 10:11 PM