Does NM Clamp Exist For This Situation? - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 11-13-2014, 04:31 PM   #16
Rewards Points: 3,396
Again. If I had an intact conduit system. I could not sleeve an Un stripped piece of nm through it. Five feet or ninety five feet?
ritelec is offline   Reply With Quote
Old 11-13-2014, 04:45 PM   #17
Alls good. I can run it through my dining room.
334.10. In dwelling unit
(A) concealed
334.15 (B) protected from physical damage (emt)
No mention of location or length
(C) is as it applies if just sleeved at the end like down the wall for protection. Pointing out securing it within 12 inches of the conduit. If it is a system box to box no need to secure
Old 11-13-2014, 04:49 PM   #18
Originally Posted by Jump-start View Post
I think you are ok. Short sections are allowed by code. As long as the cable is secured where it enters the conduit you are ok.
Not busting horns. Where does it say short section and what is the length of the short section?
Old 11-13-2014, 05:05 PM   #19
Originally Posted by Jim Ignatowski View Post
So as long as it's clamped as it enters the conduit, it doesn't need to be secured at the fixture box? It's already been secured where it enters the conduit.
I use the from to connectors also. But no from to or clamp is required. Just a strap or staple before it enters the conduit.
Old 11-13-2014, 05:13 PM   #20
Rewards Points: 226
Is there any particular reason for the 12/2 romex for a ceiling fixture ?
daveblt is offline   Reply With Quote
Old 11-13-2014, 05:21 PM   #21
Rewards Points: 1,192
I wouldn't worry about it. What type of fixture are you using?
bobelectric is offline   Reply With Quote
Old 11-13-2014, 05:26 PM   #22
Master Electrician
Rewards Points: 5,374
The cable does not need to be secured in the box since that takes place where the cable enters. As long as the transition bushing is inplace you are ok.
As for the box itself this would be a nice compliment against the metal edges:
http://www.homedepot.com/p/Halex-3-4...vZbohkZ1z117wk
Bushings are not required for NM type cables. The sheathing protects the conductors.
brric is online now   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
stickboy1375 (11-13-2014)
Old 11-13-2014, 05:27 PM   #23
Master Electrician
It doesn't.
ritelec (11-13-2014)
Old 11-13-2014, 05:41 PM   #24
Rewards Points: 1,832
I know, but I toss one on anyway. A good idea.
Jump-start is offline   Reply With Quote
Old 11-13-2014, 05:58 PM   #25
It doesn't make reference to short sections but gives specifics on it. I will see if I can find the code sections.
Old 11-13-2014, 06:03 PM   #26
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
In your opinion, but it's not required, nor serves any purpose except to make you feel warm and happy.
Old 11-13-2014, 06:04 PM   #27
Yes, from a code perspective not required for NM or that size of wire. Since when is DIY chatroom the race to code minimum?
Old 11-13-2014, 06:05 PM   #28
Banned Electrician
HARRY304E's Avatar
Rewards Points: 204
The cable is considered supported and secured because it's in pipe so like the others said you do not need a clamp in the box.
"Government is not the solution to our problem; Government is the problem."
HARRY304E is offline   Reply With Quote
Old 11-13-2014, 06:06 PM   #29
E2 Electrician
Yes, from a code perspective not required for NM or that size of wire. Since when is DIY chatroom the race to the code minimum?
The bushing serves no purpose, I never mentioned anything about code.
Old 11-13-2014, 06:07 PM   #30
''Not required" I thought you meant code.
Tags
clamp , conduit , romex
Some items work, some items don't (or a very wacky situation) gameboy9 Electrical 21 04-22-2013 10:50 AM
possible violation- 2 cables in single clamp? drgkjd Electrical 5 05-29-2010 04:06 PM
Clamp Meter Findings jamiedolan Electrical 16 09-08-2008 08:13 PM
Challenging situation, please help. jaes HVAC 4 07-06-2008 06:48 AM
Clamp on Amp Tester Help stagger19 Electrical 3 03-07-2007 08:26 PM