I'm hoping that someone can provide a suggestion for a NM clamp that will work in this situation. This metal conduit is going to a ceiling fixture. I'm looking for a method to secure the cable as it enters the box.
I attached a picture to illustrate. Thank you in advance.
Does NM Clamp exist for this situation?-img_6958.jpg   Does NM Clamp exist for this situation?-img_6961.jpg
Jim Ignatowski is offline   Reply With Quote
Old 11-13-2014, 03:51 PM   #2
Rewards Points: 1,306
No. You can't run NM inside EMT.
curiousB is offline   Reply With Quote
Old 11-13-2014, 03:55 PM   #3
Rewards Points: 1,832
Depends on the length. A short section is ok provided it has a clamp on the transition point.
Jump-start is offline   Reply With Quote
Old 11-13-2014, 03:55 PM   #4
Master Electrician
Rewards Points: 5,374
Totally false.
brric is online now   Reply With Quote
The Following 8 Users Say Thank You to brric For This Useful Post:
jbfan (11-13-2014), Jim Port (11-13-2014), jproffer (11-13-2014), PaliBob (11-13-2014), ritelec (11-13-2014), rjniles (11-13-2014), Speedy Petey (11-13-2014), stickboy1375 (11-13-2014)
Old 11-13-2014, 03:57 PM   #5
Master Electrician
Originally Posted by Jim Ignatowski View Post
Hello,
Remove the sheathing and leave at least 1/4" extended inside the box.
Old 11-13-2014, 04:02 PM   #6
This is one code allowance (just remember it is for indoor scenarios only):
Does NM Clamp exist for this situation?-clipboard01ne3c.jpg   Does NM Clamp exist for this situation?-nec2.jpg
The Following User Says Thank You to Jump-start For This Useful Post:
Old 11-13-2014, 04:05 PM   #7
Rewards Points: 219
This is a very short run of EMT, maybe 6' of metal conduit and it's 3/4" ... The cable is clamped as it leaves the wall, but I was hoping to secure it at the box too. I'm aware of the debate about romex in conduit, but I was unaware this was a violation. My only other alternative is to tear down my ceiling and drill through a number of cross beams.
Old 11-13-2014, 04:06 PM   #8
Rewards Points: 219
This is an interior dry location ... Garage ceiling.
Old 11-13-2014, 04:08 PM   #9
Very good.
This, or something similar would need to be put on the beginning of the conduit where the cable transitions:
http://www.homedepot.com/p/Raco-1-2-...vZbohkZ1z117vg
Old 11-13-2014, 04:12 PM   #10
I think you are ok. Short sections are allowed by code. As long as the cable is secured where it enters the conduit you are ok.
Old 11-13-2014, 04:12 PM   #11
Rewards Points: 219
So as long as it's clamped as it enters the conduit, it doesn't need to be secured at the fixture box? It's already been secured where it enters the conduit.
Old 11-13-2014, 04:15 PM   #12
The cable does not need to be secured in the box since that takes place where the cable enters. As long as the transition bushing is inplace you are ok.
As for the box itself this would be a nice compliment against the metal edges:
http://www.homedepot.com/p/Halex-3-4...vZbohkZ1z117wk
Old 11-13-2014, 04:18 PM   #13
Rewards Points: 219
Yes, that makes a lot of sense, I'll add those. Thanks a lot for the help.
Old 11-13-2014, 04:19 PM   #14
Welcome
Old 11-13-2014, 04:29 PM   #15
Rewards Points: 3,396
Hold on.
If I wanted to do this across my finished basement or I wanted to do this across my dining I couldn't.
ritelec is offline   Reply With Quote
Tags
clamp , conduit , romex
Some items work, some items don't (or a very wacky situation) gameboy9 Electrical 21 04-22-2013 10:50 AM
possible violation- 2 cables in single clamp? drgkjd Electrical 5 05-29-2010 04:06 PM
Clamp Meter Findings jamiedolan Electrical 16 09-08-2008 08:13 PM
Challenging situation, please help. jaes HVAC 4 07-06-2008 06:48 AM
Clamp on Amp Tester Help stagger19 Electrical 3 03-07-2007 08:26 PM