Old 03-10-2010, 03:12 PM   #16
Master Electrician
Rewards Points: 5,082
Originally Posted by mopowers View Post
I'm not sure of the wire size. But it would be whatever size needed for a 50amp circuit. I do know that the wire is aluminum. It looks really big to my untrained eye.
How old is the circuit? Could it be tinned copper rather than aluminum?
brric is offline   Reply With Quote
Old 03-10-2010, 03:21 PM   #17
Master Electrician
Assuming #4 Al:
VD for 17 amps @240 volts is 0.5 volts or 0.4%
VD for 34 amps @120 volts is 1 volt or 0.8%
Both of these are withinn acceptable limits.
The Following User Says Thank You to brric For This Useful Post:
mopowers (03-10-2010)
Old 03-10-2010, 03:24 PM   #18
Rewards Points: 252
I guess it could be. I have no idea. How would I tell? The house was built last July in CA if that matters.
mopowers is offline   Reply With Quote
Old 03-10-2010, 03:26 PM   #19
Rewards Points: 252
Assuming #4 Al:
Thanks man. So the difference would only be 0.4% I'm guessing I would never see that in my wallet.
Old 03-10-2010, 03:29 PM   #20
Master Electrician
The power used is the same. There is no savings differential!!!!!!!!!!
Old 03-10-2010, 03:44 PM   #21
Rewards Points: 252
You're right. Thanks!
Old 03-10-2010, 05:46 PM   #22
Civil Engineer
Rewards Points: 5,246
There is a small difference in total power consumption due to the greater losses in a circuit running at 120 volts versus 240 volts. The power consumption of the compressor does not change, however some power is consumed in the wiring up to the compressor. The power dissipated by a wire can be computed from the equation P = I * I * R where I is the amperage and R is the resistance of the wire in ohms.
The current I for a 120 volt circuit is twice that for an equivalent power 240 volt circuit. The resistance of the wire is essentially independent of the voltage, but does depend on the size of the wire. Therefore the power loss in a 120 volt circuit is 4 times the power loss of an equal length 240 volt circuit if the wire is sized for the amperage draw at 120 volts. If the wire at 240 volts is sized for 240 volts, you will probably use a smaller wire than the 120 volt case, and the resistance is higher, but the square factor of the amperage typically overcomes the somewhat higher resistance, and you still dissipate more power. Remember, you pay for the power loss in the wiring up to the device.
Example: A compressor designed for 17 amps at 240 volts would require #12 wire, at 34 amps at 120 volts you would use #8 wire. #12 Cu wire has a resistance of 0.159 ohms/100 ft, while #8 wire has a resistance of .063 ohms/100 ft. Assuming a 100 ft run, the losses in the wire are as follows:
120 volts: 34 x 34 x .063 = 73 watts
240 volts: 17 * 17 * .159 = 46 watts
In this case, the 240 volt circuit saves 27 watts of power.
Old 03-10-2010, 05:58 PM   #23
Master Electrician
You are assuming different sizes of wire which is not what has been discussed here.
Old 03-10-2010, 07:08 PM   #24
Electrical Contractor
kbsparky's Avatar
It is a valid assumption, since the original question postulated using the same compressor wired at different voltages. Even with the larger sized wire for the 120 Volt connection, you still save a few watts wiring it for 240 Volts.
If one were to use the larger conductor wired for 240 Volts, one could argue that more watts could be saved. But the difference would not be worth it.
The rule of thumb on this or any other motor load is always use the highest available voltage when installing such circuits.
-KB
240v Air Compressor to 120v help ruacoltsnut General DIY Discussions 10 11-11-2010 04:05 PM
Pulling 120V outlet from a 240V circuit? npage148 Electrical 12 11-08-2009 11:29 AM
Do you think a tool running at 240v works better than at 120v? Piedmont Electrical 39 07-03-2009 09:50 PM
Understanding 120V branch loads in 100A 240V system WaldenL Electrical 17 02-17-2009 09:15 AM
Cattle waterer 240V - also need 120v! 2wheelinusa Electrical 6 10-05-2008 06:39 PM