Old 02-22-2010, 07:49 PM   #16
Member
 
Join Date: May 2009
Location: Brooklyn, New York (NYC)
Posts: 1,124
Rewards Points: 500
Thumbs up


KB sparky (Poster #15) This whole discussion revolved around single Phase. In Three Phase, where you are dealing with (Triplen ) Harmonics, not only does the Neutral carry only the unbalanced load. But it triples, and overloads the Neutral. One of the solutions for that problem is to have a (much) heavier Neutral than the Hot wires. Even having a lot of electronic Ballasts can create (Triplen) Harmonics.
Quote:
Originally Posted by rovers1973 View Post
Thanks Darren,
I was planning on having the pvc come up from the ground to the bottom of the meter base, and the feeder wires going through the back to the panel inside? Am I wrong in thinking I won't have and LB?? Or am I just confused here.

I am using emt between the meter and panel, and I have the locknuts and the ground bushing already. By plastic bushing, do you just mean the push in type that go inside the emt fitting to stop the wire rubbing? The ground bushing itself has a plastic sleeve inside already.
spark plug is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 02-22-2010, 08:43 PM   #17
nap
You talking to me?
 
nap's Avatar
 
Join Date: Dec 2007
Location: sw mi
Posts: 7,551
Rewards Points: 6,290
Default


Quote:
Originally Posted by kbsparky View Post
One requirement of holding a master's electrical license around here is that we are compelled to take continuing education classes. :
Does that imply you believe that nobody else takes continuing ed courses?

Quote:
These classes are mainly administered by the local inspection agencies, who have Code experts on staff that evaluate the NEC and develop the courses for continuing education requirements.
Oh, you want to compare:

Let's see, one of our instructor is on a NEC code panel, one has a Ph.D. in some branch of engineering, and 2 others authored a book that is used in some apprenticeship programs. Plus one of the guys used to be a inspector.

and just as a side note, some of the classes a couple of the guys put on are so well respected that they have graduate students from the University of Notre Dame school of Engineering attend some of the classes.

So, you want to argue about who has what knowledge available to them?

so, back to my question to you: provide an installation that would allow a #4 neutral on a 200 amp single phase service.
nap is offline   Reply With Quote
Sponsored Links
Advertisement
 
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sharing Neutrals on the same phase electro Electrical 30 08-12-2010 02:10 PM
question on the "stubbie" bonding links n175h Electrical 12 10-13-2009 04:09 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 04:58 PM
Use a reduced neutral on 200a UG service ?? bradsguns Electrical 3 06-09-2008 08:00 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 11:33 AM




Top of Page | View New Posts