Derating When >2 Wires Together - Electrical - DIY Chatroom Home Improvement Forum
Old 01-30-2010, 04:07 PM   #1
Derating when >2 Wires together
I've already mentioned about my workshop circuits where I ran 10/2 & 12/2 for a 20 amp & 15 amp circuit. At one point, the circuit runs through some studs. When I drilled the holes for the studs, I drilled them to the max size allowed (at the time, I looked it up and I beleieve that was 3/4") because I expect to run another wire through the same hole when I wire the den on the other side of the wall.
But as I understand it, if you have more than 2 cables running through studs together (in this case for a distance of about 6'-8'), you are supposed to derate the cables.
While I don't have the tables to show how to derate the cables, I assume that by having them one size larger than required, I'm already good for the current circuits.
But what about when I add the third? I plan it to be a 20 amp circuit. Am I going to HAVE to use 10/2 for the 20 amp circuit (at least for the part that runs through the wall with these other two cables)?
HooKooDooKu is offline   Reply With Quote
Old 01-30-2010, 04:29 PM   #2
Licensed Pro
You do not have a problem. It is only when you get more than 9 conductors that derating affects the breaker/wire size. And with cable, it will only have an effect if you apply fire caulk to the hole.
Switch Junction box has 3 sets of 3 wires. Can't get dimmer to work knockout Electrical 14 01-10-2015 09:08 AM
Can't find the wires! brianmarsh Home Theater 2 01-24-2010 07:11 AM
Unfused connectors MELTED House wires WHAT TO DO??? jamiedolan Electrical 63 02-12-2009 06:01 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
Two black wires with one white! Please help! ibs325 Electrical 15 11-18-2007 09:38 PM